Electrical installation design guide - Table F5

I can't find where they got the infomation in this table from. 

I have checked ENA engineering recommendation P29 but there does not seem to be any tables. 

I would like to find out the resistance and reactance of a 2500kva transformer.

Parents
  • If you have a specific transformer in mind, then by far the most accurate method is to contact the owners (usually the DNO) or the maker if that can be determined - there should be a rating plate somewhere. However, in recent decades such things have been standardized by EU  regulations on efficiency, and that in turn means that the data for any transformer of the same wattage and construction will be similar. Is the transformer oil filled or solid resin ?

    FWIW, I have a 2013 copy of the guide and that refers to a table D6 of  an ENA guide P 28 - it may be that the original reference material has been superseded and later versions have not caught up ?.

    Mike

Reply
  • If you have a specific transformer in mind, then by far the most accurate method is to contact the owners (usually the DNO) or the maker if that can be determined - there should be a rating plate somewhere. However, in recent decades such things have been standardized by EU  regulations on efficiency, and that in turn means that the data for any transformer of the same wattage and construction will be similar. Is the transformer oil filled or solid resin ?

    FWIW, I have a 2013 copy of the guide and that refers to a table D6 of  an ENA guide P 28 - it may be that the original reference material has been superseded and later versions have not caught up ?.