Why 70V rms and not 50V rms - O-PEN faults

Hi, always follow this forum as such a great source, so my first time with a question, hoping someone can advise.

Why `voltage between the cpc and earth exceeding 70V rms` for Reg. 722411.4.1 (iii) and not 50V as in Reg. 411 touch voltage threshold. Is 70V deemed acceptable ?

Parents
  • 25V lasted a lot longer than that - blue cover 16th Ed (2001) section 605 (Agricultural) modifies the usual RA Ia ≤ 50V to 25V and likewise for supplementary bonding has R  ≤ 25/Ia

    Ditto for constructon sites (604).

    And even longer than that. BS 7671:2018+A2:2022 in fact.

    See Regulation 710.411.3.2.5, applies to ADS for all methods of protection against electric shock that use ADS, and Regulation 710.415.2.2 (esp NOTE).


    It's also used in hazardous areas of filling station installations, which, whilst the hazardous area installation is outside the scope of BS 7671, is covered by the APEA/EI 'Blue Book'.

Reply
  • 25V lasted a lot longer than that - blue cover 16th Ed (2001) section 605 (Agricultural) modifies the usual RA Ia ≤ 50V to 25V and likewise for supplementary bonding has R  ≤ 25/Ia

    Ditto for constructon sites (604).

    And even longer than that. BS 7671:2018+A2:2022 in fact.

    See Regulation 710.411.3.2.5, applies to ADS for all methods of protection against electric shock that use ADS, and Regulation 710.415.2.2 (esp NOTE).


    It's also used in hazardous areas of filling station installations, which, whilst the hazardous area installation is outside the scope of BS 7671, is covered by the APEA/EI 'Blue Book'.