Emergency Lux Levels in fornt of a DB

Good morning

Excuse my question if it sounds a bit naive

What is the Emergency Lux Level we need in front of a Distribution Board?

I always thought this was a case of 15lux (high risk area) however checking again BS5266 I cannot verify it unless its in front of my eyes and I am missing it.

Thanks

Parents
  • It's quite well hidden. "and adjacent to main control equipment associated with the provision of normal and emergency lighting.

    regards burn

Reply
  • It's quite well hidden. "and adjacent to main control equipment associated with the provision of normal and emergency lighting.

    regards burn

Children
  • Ah yes - so not all DBs, just the lighting ones. Which makes sense - there may not be any lighting ones in some situations - indeed sometimes it may not even be in a building at all in the conventional sense.

    Mike