Repost - Earth Rod not taken account in TN systems

Hi All,

I realise the function of the earth rod in a TN system is to provide a close reference to true earth for the neutral

The thing that has confused me slightly is the TNCS PNB, which has an earth rod located at the consumer end. When i looked at the old forums there was a debate between whether this was TNCS or TNS, as the neutral carries no current due to the earth rod, and therefore by definition cannot be a combined conductor. If the current is not dissipated into the ground via the rod, why would no current flow in the neutral of this system prior to the rod

Thanks in advance

EDIT: My question wasn’t phrased very well and I’ve tried to clean it up for future readers, but i think this is the correct summary.

Fault current CAN flow between the neutral/earth link and the neutral point of the transformer in a PNB earthing arrangement. The previous forum posters were essentially saying is that even though though the link is remote, fault current will still flow in the CNE cabling, but we can note that it also would in a pure TN-S system but more likely an internal section of busbar within the TX and the neutral bar, instead of external cabling and by that logic TN-S would be a form of TN-C-S if semantics were involved.

Link to thread

 What earthing arrangement is this? 

Parents
  • Hi, I did try and answer your previous post. The absence of current flow in the neutral of this system before the rod is due to the lack of potential difference between the neutral and the earth at that point. The PEN conductor is earthed at multiple points along its length, so it has a very low earth impedance. Consequently, there is no voltage drop along the PEN conductor, and no current flow between the PEN and PE conductors.

  • if the neutral is controlled and the risk of loss is low

    indeed - but turning that on its head if you cannot see/inspect it's full length maybe it isn't low risk so a transformer on your land, with no underground LV joints or overhead LV singles is OK - but anything else, well it becomes a matter of judgment, and recent NIC and NAPIT advice has been treat PNB like PME if in any doubt at all - which is probably sensible from their liability reduction perspective. Less useful if it is already there and you are wondering what to connect.

    Mike

  • I do consider PNB to be TN-S like, or at least more like TNS than TNC-s  I may be a minority !

    The part between the transformer star/ neutral and the first electrode is carrying current that is in perfect balance with the phase current (s) so In that sense it is carrying the fault current as well as the load current.  However, the same is true somewhere in the neutral path of a 'pure' TN-S as well.

    But the severity of breaking that extended transformer neutral connection is not the same as breaking a PEN in between two earthing points in a TNCs or PME system, as there is no-where that the chassis of equipment become live relative to terra-firma, In fact in a single phase PNB system, if you break the transformer neutral it is all quite safe, in a 3 phase PNB less so, delta connected loads will be fine but star connected ones will fight to pull the neutral off- balance. Again, the same risk is true of breaking the neutral in  TN-S.

    For me at least the thing that makes PME what it is is the 'M' - the multiple points where N and E meet. This is both the strength and the weakness - for if the CNE breaks between 2 such points then a lot of earthed metalwork is now very metallically connected to an off- earth voltage. This does not happen in TNS or PNB, regardless of which side of the one and only NE bond you sever the neutral.

     For me one could take a TNS and slide the point of separation along away from the TX, and it becomes PNB at some point,

    Also TNC-s is not always the same as PNB either, as we do not take the CNE all the way to the consuming loads or even multiple loads and split it there - the split is very much done at the origin of the distribution side of things.

    Mike.

  • My position is that PME and PNB are both subtypes of the TN-C-S earthing system. As you know, TN-C-S stands for Terra Neutral Combined Separate, which means that the supply conductor serves as both the neutral and the protective conductor, while the installation has separate conductors for these functions. The supply conductor is called PEN (Protective Earth Neutral) or CNE (Combined Neutral Earth), and the installation conductors are N (Neutral) and PE (Protective Earth) or CPC (Circuit Protective Conductor). The difference between PME and PNB lies in how the PEN or CNE conductor is earthed along the distribution network. In PME, the PEN or CNE conductor is earthed at multiple points, such as at the transformer, at the service cut-out, and at various places along the cable route. This reduces the resistance of the PEN or CNE conductor to Earth, and also provides a low-impedance path for fault currents to return to the source. However, this also creates a potential danger of touch voltage, which is the voltage difference between an exposed-conductive-part of an installation and a nearby earthed object, such as a metal water pipe or a fence. In PNB, the PEN or CNE conductor is earthed at only one point, which is far away from the transformer, between the transformer and the supply terminals of the consumer. This means that there is no other earth electrode along the cable route, and the resistance of the PEN or CNE conductor to Earth is higher than in PME. This reduces the risk of touch voltage, but also increases the risk of overvoltage, which is the voltage rise on the neutral conductor due to an open-circuit fault in the PEN or CNE conductor as you mentioned.

  • In PME, the PEN or CNE conductor is earthed at multiple points, such as at the transformer, at the service cut-out, and at various places along the cable route.

    I think of PNB as being PME for one consumer on the basis that there is nowhere for the multiple earths to be planted.

  • Good point, makes sense.

  • ‘ECA Technical Guidance: When is TN-C-S PME and when isn’t it?’ States that if the neutral is controlled and the risk of loss is low in a true PNB System, it can be treated as per TN-S and TNCS PME bond sizes are not required

    Interesting. Whilst that is true for private LV supplies (or where a private transformer is used), it doesn't align with ENA EREC G12/5 (and G12/4 before it) which states that PME conditions apply to PNB where the PNB earthing arrangement is in the distribution system. This is a very important consideration.

  • My position is that PME and PNB are both subtypes of the TN-C-S earthing system.

    That is definitely not always the case (regardless of whether we are talking about PNB in the public network, or from a private transformer. It's possible to arrange armour of cables so it's TN-S all the way pretty much!

  • I think of PNB as being PME for one consumer on the basis that there is nowhere for the multiple earths to be planted.

    This isn't true, PNB can supply up to 4 customers if used by DNO. There are different variants on how earthing is arranged, and whether a CNE (combined neutral-and-earth) is provided to the customer (and connected to the MET) or SNE (separate neutral-and-earth).

  • PME and PNB are both variants of the TN-C-S earthing system, where the PEN conductor is split into separate neutral and earth conductors at the consumer’s premises. The main distinction is that PME has multiple earthing electrodes along the supply network, whereas PNB has a single earthing electrode, typically far from the transformer . However, as you noted, it is feasible to have a TN-S earthing system throughout the entire supply chain, by employing cables with distinct protective conductors or armouring that is not connected to the PEN conductor . This would circumvent the potential issues of PME and PNB, such as perceived shock, open-circuit PEN conductor, or diverted neutral current.

  • Furthermore, some of the advantages and disadvantages of each earthing system depend on various factors, such as the type and length of the cables, the soil resistivity, the fault current magnitude and duration, and the sensitivity of the equipment. Some of the benefits of PME are that it reduces the number of conductors required, lowers the impedance of the fault loop, and improves the voltage regulation. However, some of the drawbacks of PME are that it increases the risk of touch voltage and transferred potential, requires special precautions for extraneous conductive parts, and may not be suitable for certain locations or applications. Some of the benefits of PNB are that it eliminates the risk of transferred potential, simplifies the earthing arrangements, and reduces the interference with communication systems. However, some of the drawbacks of PNB are that it increases the impedance of the fault loop, worsens the voltage regulation, and may cause problems with harmonic currents or neutral displacement.


    A TN-S system can overcome some of these limitations by providing a separate protective conductor from the source of supply to the consumer’s installation. This ensures that there is no connection between the neutral and earth conductors anywhere in the network, and that each protective conductor is connected to an individual earthing electrode at each point of use. This provides a high level of safety and reliability for electrical installations, as well as compatibility with sensitive equipment. However, a TN-S system also has some disadvantages, such as requiring more conductors and materials, increasing the cable size and weight, and posing difficulties in retrofitting existing installations.


    Therefore, there is no definitive answer to which earthing system is better or worse in general. The choice depends on the specific circumstances and requirements of each installation. A careful analysis and comparison of the technical and economic aspects of each earthing system is necessary to make an informed decision.

Reply
  • Furthermore, some of the advantages and disadvantages of each earthing system depend on various factors, such as the type and length of the cables, the soil resistivity, the fault current magnitude and duration, and the sensitivity of the equipment. Some of the benefits of PME are that it reduces the number of conductors required, lowers the impedance of the fault loop, and improves the voltage regulation. However, some of the drawbacks of PME are that it increases the risk of touch voltage and transferred potential, requires special precautions for extraneous conductive parts, and may not be suitable for certain locations or applications. Some of the benefits of PNB are that it eliminates the risk of transferred potential, simplifies the earthing arrangements, and reduces the interference with communication systems. However, some of the drawbacks of PNB are that it increases the impedance of the fault loop, worsens the voltage regulation, and may cause problems with harmonic currents or neutral displacement.


    A TN-S system can overcome some of these limitations by providing a separate protective conductor from the source of supply to the consumer’s installation. This ensures that there is no connection between the neutral and earth conductors anywhere in the network, and that each protective conductor is connected to an individual earthing electrode at each point of use. This provides a high level of safety and reliability for electrical installations, as well as compatibility with sensitive equipment. However, a TN-S system also has some disadvantages, such as requiring more conductors and materials, increasing the cable size and weight, and posing difficulties in retrofitting existing installations.


    Therefore, there is no definitive answer to which earthing system is better or worse in general. The choice depends on the specific circumstances and requirements of each installation. A careful analysis and comparison of the technical and economic aspects of each earthing system is necessary to make an informed decision.

Children
No Data