Repost - Earth Rod not taken account in TN systems

Hi All,

I realise the function of the earth rod in a TN system is to provide a close reference to true earth for the neutral

The thing that has confused me slightly is the TNCS PNB, which has an earth rod located at the consumer end. When i looked at the old forums there was a debate between whether this was TNCS or TNS, as the neutral carries no current due to the earth rod, and therefore by definition cannot be a combined conductor. If the current is not dissipated into the ground via the rod, why would no current flow in the neutral of this system prior to the rod

Thanks in advance

EDIT: My question wasn’t phrased very well and I’ve tried to clean it up for future readers, but i think this is the correct summary.

Fault current CAN flow between the neutral/earth link and the neutral point of the transformer in a PNB earthing arrangement. The previous forum posters were essentially saying is that even though though the link is remote, fault current will still flow in the CNE cabling, but we can note that it also would in a pure TN-S system but more likely an internal section of busbar within the TX and the neutral bar, instead of external cabling and by that logic TN-S would be a form of TN-C-S if semantics were involved.

Link to thread

 What earthing arrangement is this? 

Parents
  • PME and PNB are both variants of the TN-C-S earthing system, where the PEN conductor is split into separate neutral and earth conductors at the consumer’s premises.

      , this isn't quite true.

    Even in some public PNB systems, the distributor provides an SNE cable.

    WPD, at least, used to publish this openly.

    The key differentiator, is that the transformer star point (or mid-point) is NOT earthed directly in PNB systems (whatever the variant), but is in true TN-S and TN-C-S, but the N conductor is connected elsewhere from the transformer.

    You can then argue whether the "N" conductor (I will not call it a Neutral at this juncture, because strictly, according to the International Electrotechnical Vocabulary, it's perhaps not a Neutral in single-phase or split-phase secondary transformers) in a PNB system acts as a PE conductor for the transformer itself ... but the wiring (which is what BS 7671 is concerned with) can be SNE, and therefore it's possible for PNB to be TN-S (but PME conditions would still apply).

    The following diagrams might help illustrate what I'm talking about:

  • There are further (minor) variations in the above between the DNO's (and before that the old 'Electricity Boards').

    A small number (typically 4) of consumers may be supplied by each of the PNB variants.

    In 'variant 2', sometimes each customer has their own electrode, sometimes only the first, or first and last.

Reply
  • There are further (minor) variations in the above between the DNO's (and before that the old 'Electricity Boards').

    A small number (typically 4) of consumers may be supplied by each of the PNB variants.

    In 'variant 2', sometimes each customer has their own electrode, sometimes only the first, or first and last.

Children
  • Hello Graham, I have drawn my conclusions from the following reliable sources, which support my statement that PME and PNB are both variants of the TN-C-S earthing system, where the PEN conductor is split into separate neutral and earth conductors at the consumer’s premises:
    The [Electricity Safety, Quality and Continuity Regulations 2002] stipulate that a TN-C-S system is “an earthing system having a common conductor throughout the system which is used to carry both earth fault current and the neutral current of that system, and in which the voltage of that conductor is kept substantially at earth potential by connecting it to earth at one or more points”. This stipulation applies to both PME and PNB systems, as they both employ a common conductor (PEN or CNE) that carries both earth fault current and neutral current, and is connected to earth at one or more points.
    The [IET Wiring Regulations (BS 7671:2018)] specify that a TN-C-S system is “a system having one or more points of the source of energy directly earthed, the exposed-conductive-parts of the installation being connected to that point by protective conductors”. This specification also applies to both PME and PNB systems, as they both have one or more points of the source of energy directly earthed (the neutral of the source in PME and the PEN or CNE conductor in PNB), and the exposed-conductive-parts of the installation being connected to that point by protective conductors (the metallic sheath or armour of the service cable in PME and the separate protective conductor or CNE conductor in PNB).
    [The Electrician’s Guide To The Building Regulations] state that PME and PNB are both variants of TN-C-S systems, where “the distributor provides a combined neutral and protective conductor (PEN) up to a point near to the consumer’s installation. At this point, separate neutral (N) and protective (PE) conductors are provided for connection to the consumer’s installation”. This statement corresponds to both PME and PNB systems, as they both have a PEN or CNE conductor up to a point near to the consumer’s installation, where it is split into separate neutral and earth conductors. Therefore, based on these sources, I uphold that my statement is accurate and consistent with the definitions and descriptions of TN-C-S earthing systems. However, I highly respect your opinion and suspect you are right. I also invite any further evidence or arguments that contradict my claim.

  • Agreed, but regards your first point:

    Hello Graham, I have drawn my conclusions from the following reliable sources, which support my statement that PME and PNB are both variants of the TN-C-S earthing system, where the PEN conductor is split into separate neutral and earth conductors at the consumer’s premises:

    That is true of 'variant 2' in my diagrams, but NOT 'variant 1' which is split earlier than the consumer's premises.

    And the last point.

    [The Electrician’s Guide To The Building Regulations] state that PME and PNB are both variants of TN-C-S systems, where “the distributor provides a combined neutral and protective conductor (PEN) up to a point near to the consumer’s installation. At this point, separate neutral (N) and protective (PE) conductors are provided for connection to the consumer’s installation”. This statement corresponds to both PME and PNB systems, as they both have a PEN or CNE conductor up to a point near to the consumer’s installation, where it is split into separate neutral and earth conductors.

    Variant 2, the distributor provides a separate N and PE, not a PEN.

    It certainly is not that clear cut at all.

    EXCEPT that G12/5 says that PME conditions apply where PNB is used (that would be for Variant 1 and Variant 2 - although strictly only variant 2 is always TN-C-S).

    There's a little more to this, being the fact that the Neutral (as we use it in most of BS 7671) isn't always a "neutral" ... especially in single-phase systems (i.e. where the LV supply transformer is single-phase).