Generator earthing....Again!

Hi All,

We've just installed a 400A manual changeover switch for a client that requires a backup generator (Not permanently installed - as It's being supplied by a generator hire company as and when there are power outages) It's a semi rural location and they seem to get power cuts several times a year.

The generator company aren't being particularly forthcoming with information regarding the sets they will be supplying (Other than saying they all have in built earth fault Leakage protection) 

The existing supply is TNCS & I know we can't rely on the DNO earthing during a power cut. With this in mind and little more information to go on from the generator company,  Should we be installing a Rod(s) and just ensuring we have a resistance lower than 20 Ohms.  Is there anything else I need to consider, Obviously my concern is ensuring that any existing protective devices will still operate under fault conditions whilst supplied by the generator.

Given that  411.4.2 now recommends an electrode at the point of supply, I assume we have no real issue with a combined  TT / TNCS arrangement!

All thoughts are more than welcome,

Thanks,

Tim

Parents
  • Right chaps/ladies- this seems to be an appropriate place and thread to get educated better in my understanding. 

    Please may someone help me and my understanding of generator earthing requirements. 

    I don't do Generators all day every day, but periodically do for construction site set ups and temporary supplies for construction site compounds. This is not my day in and day out job, but not uncommon either. 

    So most Generators larger than 10KVa arrive as standard, here in the UK as a TNS system. I believe that is standard operating procedure around here.

    So far all mine have. Hired from Large national hire companies.

    So the generator runs and operates as a TNS System. Earth fault path is a TNS system. 

    However, I understand if the Generator is NOT earth staked, the neutral and earth systems, because they are common at the Genset - can float up and down with reference to terra firma - the ground next to the Generator - and RCDs don't know when a fault is occurring as this floating value confuses the RCDs......, yes?

    All of my generators have come with a earth fault relay RCDs that I'd normally set up, (I commonly call these "viggi units") as described in the above sort of way, with a 300mA 0.25 second time delay and cascading RCD settings out from there.

    Clearly, this needs to have an earth reference point to tell the RCD what value earth is. Of course it does - no dispute there. 

    So - I think I'm all on track so far......

    Now, to the earth reference point; the earth stake, matt, or commonly for me, on railway sidings or construction sites out in the country side where a metal fence has been installed, a metal fence that is "owned by" and managed by us, and I have permission to use - then I'd use the metal fence, I like a metal fence................... and its required value in ohms.

    So, hypothetically,  lets pretend that the generator was laid on a glass slab, or floating in the air - no contact with the ground at all, and the earth reference point (The earth stake hammered into the ground and connected to the Generator earth point for example) is effectively an infinite value as an earth fault path back to the Generator, but it does provide the earth part of the generator with a reference point to what the earth value should be. I understand that the earth fault relay RCD "viggi" unit would function perfectly well.

    So to my question - why should we try to achieve a 20 ohm value for this earth reference point - its just an earth reference and not an earth fault path - surely? 

    (Obviously I'm not talking about a TT system here - I understand the need for that earth stake to be less than 200 ohms and all its difficulties, I think)

    If the generator earth reference point was 200 ohms or 2000 ohms, would it make a difference? I don't think so.....

    I feel an ohms Law coming on as the explanation here.........(V=IR maybe?)

    But it's not a fault path, just a reference point........Education required please.

    If i stuck a good old metal shaft screw driver in the ground it'd (The RCD part of the Genny) probably function perfectly well surely?

  • Your understanding is sound, but there are a couple of extra situations to consider,

    1)

    Actually even without the earth rod there is merit in the RCD for 'glass slab' systems, or vehicles on tyres as we more commonly find the nearest approximation to that - the CPC may bond solidly to the chassis but a human in between an exposed  live and the vehicle body at potential of the system CPC is a few k ohms and will not trip an MCB.

    But an RCD sees the current coming back via the CPC as 'missing' from the expected neutral current, and trips on the imbalance between L and N current in the normal way.

    2) 20 ohms is a bit arbitrary but it cannot be too high - now our genset is on the ground and the earth rod is in the dry and not a great contact.  Any fault to that connects live to terra-firma (wire pinched on the rigging of a lighting tower, socket box falls into a ditch full of water...) will cause current into the Terra-firma at the fault, and back out of terra firma back to the genset star point at the genset earth electrode. This current raises the genset case and the rig CPC relative to terra-firma, and we do not want the rise to be too painful for anyone leaning against any 'earthed' metalwork connected to the genset CPC loop.

    With a 300mA and delay set on the 'Viggy'  unit, 0,2 amps (plus some) could be flowing all day, so a hundred ohms would give a rise of 20V plus and 200 ohms would be 40V or more and some rise. 2000 ohms would never operate that RCD.


    A safety factor of ten from a 50V rise with the highest common RCD setting is a very safe starter for ten with a lot of allowance for seasonal variation and corrosion.. but  yes, 20 ohms is to be seen as an aspiration, not an essential.

    Mike

  • If the generator earth reference point was 200 ohms or 2000 ohms, would it make a difference? I don't think so.....

    Well, funny you should pick 200 ohms ... Note to Table 41.5 of BS 7671 tells us that above 200 ohms, an earth electrode may not be stable - a physical fact, which rules out 2000 ohms.

    Interestingly, since 1st Ed of the IET CoP for Electrical Energy Storage Systems, for "small" battery storage/PV systems (say up to 10 kVA total generation), 200 ohms (the limit of stability) is often seen as the limit. In the 2nd Ed, the 10 kVA "limit" above which 20 ohms max earth electrode resistance is required was removed, and this has remained in the 3rd Ed - all "prosumers installations" should have an earth electrode not exceeding 200 ohms.

    So it seems your line of thinking is in line with the experts involved in that Code of Practice. (Note also, though, with the application of prosumer's electrical installations, unless the system is TT, the consumer's earth electrode will usually be in parallel with the distributor's means of earthing, so unless the supply cable is being worked on, more often than not the effective earthing resistance of the installation is lower in any case.)

    As you've already identified, there is an exception for TT systems if there are any TT circuits supplied from the system, the total loop impedance (based on the RCD residual current rating) should not exceed the values in Table 41.5 of BS 7671.



    So, yes, you are correct, a value of greater than 20 ohms may be acceptable, but the value ought not to exceed 200 ohms.

    BSI have announced a project to revise BS 7430, which is under way, so it will be interesting to see if there is any movement on the basic "20 ohms" that is currently recommended.

  • lets pretend that the generator was laid on a glass slab, or floating in the air

    You don't have to imagine too hard - look at section 717 for mobile/transportable units - we can have exactly that situation.

       - Andy.

Reply Children
  • You don't have to imagine too hard - look at section 717 for mobile/transportable units - we can have exactly that situation.

    Note though that in this instance, if leads are run outside the unit, and damaged such that a line conductor becomes connected to Earth (the ground - or something metal in good contact with the ground), then the frame/chassis/container of the unit becomes LIVE, and no protective device would operate ... except strategically-placed RCDs but even then only after someone touches the live frame/chassis/container.

  • Indeed - I have seen exactly that - a shock from the door handles of a genset towing vehicle  parked up & supplying (from memory) radio gear and lights.

    really there is a step change between using a genset on a moving vehicle with totally enclosed loads and wiring and the same vehicle parked up and with a lead running out over the grass or electrical loads that are on the ground beside the vehicle.

    As soon as that second stage is reached, a connection to terra-firma of at least RCD trippig quality really  should accompany it.
    Mike

  • Thanks AJJewsbury....

  • Note though that in this instance, if leads are run outside the unit, and damaged such that a line conductor becomes connected to Earth (the ground - or something metal in good contact with the ground), then the frame/chassis/container of the unit becomes LIVE, and no protective device would operate

    You can get a very similar effect with a normal (e.g. DNO) supply too - a downed overhead line conductor in a puddle or just an uncleared L-PE fault in a TT installation - current flows to true Earth and returns through the generator/transformer's electrode - the current * electrode resistance producing a voltage difference between the general mass of the earth and the system's PE reference ... which is then exported to all connected TN installations.

       - Andy.

  • which is then exported to all connected TN installations.

    Yes, however in general those installations have equipotential bonding and fortuitous local earthing, so the effects are generally mitigated or limited until the condition is addressed (but OK there is a small chance of an issue).

    The big difference with the mobile/transportable unit fault discussed, is that it's immediately a potentially fatal shock risk, which will go undetected (and won't operate any protective devices) until the moment someone gets a shock ... and even then unless you have properly co-ordinated RCD protection, a protective device won't operate.

  • Yes, however in general those installations have equipotential bonding and fortuitous local earthing, so the effects are generally mitigated or limited

    Until you get to the outside tap or EV situation...

       - Andy.

  • Until you get to the outside tap or EV situation...

    At the moment, we only have evidence that this is genuinely problematic on a widespread basis for open-PEN situations, not particularly the situation you describe (it could be related to both frequency of occurrence and also the fact that effects of one are more readily noticeable than the other).

    Yes, there may be an elevated voltage in those situations, but there don't seem to be the same number or severity of instances as open-PEN. And even then I'm not aware of any deaths.

    However, compared with the "floating system with protective conductors connected to neutral point" ... whilst the damaged cable might appear to be rare, the consequences are very serious (and have happened) ... definitely a real problem with the possibility of instant death in a muddy field or on a wet construction site.