Generator earthing....Again!

Hi All,

We've just installed a 400A manual changeover switch for a client that requires a backup generator (Not permanently installed - as It's being supplied by a generator hire company as and when there are power outages) It's a semi rural location and they seem to get power cuts several times a year.

The generator company aren't being particularly forthcoming with information regarding the sets they will be supplying (Other than saying they all have in built earth fault Leakage protection) 

The existing supply is TNCS & I know we can't rely on the DNO earthing during a power cut. With this in mind and little more information to go on from the generator company,  Should we be installing a Rod(s) and just ensuring we have a resistance lower than 20 Ohms.  Is there anything else I need to consider, Obviously my concern is ensuring that any existing protective devices will still operate under fault conditions whilst supplied by the generator.

Given that  411.4.2 now recommends an electrode at the point of supply, I assume we have no real issue with a combined  TT / TNCS arrangement!

All thoughts are more than welcome,

Thanks,

Tim

Parents
  • Right chaps/ladies- this seems to be an appropriate place and thread to get educated better in my understanding. 

    Please may someone help me and my understanding of generator earthing requirements. 

    I don't do Generators all day every day, but periodically do for construction site set ups and temporary supplies for construction site compounds. This is not my day in and day out job, but not uncommon either. 

    So most Generators larger than 10KVa arrive as standard, here in the UK as a TNS system. I believe that is standard operating procedure around here.

    So far all mine have. Hired from Large national hire companies.

    So the generator runs and operates as a TNS System. Earth fault path is a TNS system. 

    However, I understand if the Generator is NOT earth staked, the neutral and earth systems, because they are common at the Genset - can float up and down with reference to terra firma - the ground next to the Generator - and RCDs don't know when a fault is occurring as this floating value confuses the RCDs......, yes?

    All of my generators have come with a earth fault relay RCDs that I'd normally set up, (I commonly call these "viggi units") as described in the above sort of way, with a 300mA 0.25 second time delay and cascading RCD settings out from there.

    Clearly, this needs to have an earth reference point to tell the RCD what value earth is. Of course it does - no dispute there. 

    So - I think I'm all on track so far......

    Now, to the earth reference point; the earth stake, matt, or commonly for me, on railway sidings or construction sites out in the country side where a metal fence has been installed, a metal fence that is "owned by" and managed by us, and I have permission to use - then I'd use the metal fence, I like a metal fence................... and its required value in ohms.

    So, hypothetically,  lets pretend that the generator was laid on a glass slab, or floating in the air - no contact with the ground at all, and the earth reference point (The earth stake hammered into the ground and connected to the Generator earth point for example) is effectively an infinite value as an earth fault path back to the Generator, but it does provide the earth part of the generator with a reference point to what the earth value should be. I understand that the earth fault relay RCD "viggi" unit would function perfectly well.

    So to my question - why should we try to achieve a 20 ohm value for this earth reference point - its just an earth reference and not an earth fault path - surely? 

    (Obviously I'm not talking about a TT system here - I understand the need for that earth stake to be less than 200 ohms and all its difficulties, I think)

    If the generator earth reference point was 200 ohms or 2000 ohms, would it make a difference? I don't think so.....

    I feel an ohms Law coming on as the explanation here.........(V=IR maybe?)

    But it's not a fault path, just a reference point........Education required please.

    If i stuck a good old metal shaft screw driver in the ground it'd (The RCD part of the Genny) probably function perfectly well surely?

  • I picked 200 ohms as that value keeps coming up in various literature for earth stakes -  I multiplied it by 10 just to get an extreme distance from the 200 ohm value and twice the human bodies apparent value.

    Another value that keeps coming up is 20 ohms - this earth stake for Generators and in the rail industry, I have done a lot of metal work bonding - with overhead HV supplies - and the 20 ohms value comes up there too. Thanks for the reply. I'm sure I've got the IET temporary power supplies booklet - bought at the Elex show - I must read it again and pay more attention. I assume it's based on BS7430. 

  • Ah - so the value of 200 ohms keeps the touch voltage to 40 odd Volts - R<50V/Ia - has been used I assume?

    Less than 200 ohms then ever less touch voltage.....

    Now - this is where my uderstanding might be falling over - if that Genny is on wheels, a glass slab or up in the air or something similar and an earth stake is installed - then there wont be a path back to the generator, via the earth stake - clearly there's a fault path via the TNS path.........and perhaps a division of fault current (depending on the resistance) -down to terra firma via the earth stake. - Like a Zs would be infinite - or as near to - if you did a live or dead test - from the Genny and tested from the Genny Live to earth stake (disconnected from the Genny MET)

    In old fashion parlance - an ELCB would work. before even my time, but obviously they're still around.

    However our modern viggi units also work, (don't they? won't they?) because the earth stake gives the RCD an earth reference to work from, and holds the Genny frame to a local earth potential - that is different to the neutral value - which is also held, now at a local earth value - and allows a current loss too - to somewhere other than the TNS fault path, and the RCD functions....

    So in this case the 20 ohms, 200 ohms, or 2000 ohms path back to the genny is irrelevant surely? only a good contact with earth? it'd give an earth reference, its not a fault path.........

    I'm still tripping over the same mis understanding.........

    Kind Regards

    Chris

  • Thanks AJJewsbury....

  • I assume it's based on BS7430. 

    The 20 ohms is from BS 7430.

    If we look back in history of electrical standards for earthing, sometimes 10 ohms has been quoted, sometimes 20 ... but never with a given reason.

    One of my [esteemed] colleagues looked into this at some length and couldn't find a definitive documented "rule of thumb" or "formula" that either 10 ohms or 20 ohms was based on (although I guess we could all come up with a variety of fault current values vs touch-voltage or touch-current using ohms law)?

  • Note though that in this instance, if leads are run outside the unit, and damaged such that a line conductor becomes connected to Earth (the ground - or something metal in good contact with the ground), then the frame/chassis/container of the unit becomes LIVE, and no protective device would operate

    You can get a very similar effect with a normal (e.g. DNO) supply too - a downed overhead line conductor in a puddle or just an uncleared L-PE fault in a TT installation - current flows to true Earth and returns through the generator/transformer's electrode - the current * electrode resistance producing a voltage difference between the general mass of the earth and the system's PE reference ... which is then exported to all connected TN installations.

       - Andy.

  • So in this case the 20 ohms, 200 ohms, or 2000 ohms path back to the genny is irrelevant surely? only a good contact with earth? it'd give an earth reference, its not a fault path.....

    It's not a fault path for a conventional ADS style L-PE fault, correct. In an additional protection kind of situation (e.g. picking up the end of a severed flex while stood outdoors) it does though. Likewise for the (rare) situations where a line conductor come into contact with true Earth without an PE conductor intervening. On larger systems you start to see stray capacitance and general leakage currents due to imperfect insulation having similar effects.

        - Andy.

  • which is then exported to all connected TN installations.

    Yes, however in general those installations have equipotential bonding and fortuitous local earthing, so the effects are generally mitigated or limited until the condition is addressed (but OK there is a small chance of an issue).

    The big difference with the mobile/transportable unit fault discussed, is that it's immediately a potentially fatal shock risk, which will go undetected (and won't operate any protective devices) until the moment someone gets a shock ... and even then unless you have properly co-ordinated RCD protection, a protective device won't operate.

  • Likewise for the (rare) situations where a line conductor come into contact with true Earth without an PE conductor intervening.

    Not so rare. That is your expensive Ho7 style  rubber 3 phase 100A extension lead  being thrown over a metal fence and snagging on a sharp edge, and striking a phase core first, or the free socket on the far end going 'splosh' as it lands on the other side .

    While in a perfect world this would not occur, it can and does happen when things are being deployed in a hurry and / or  in bad light.

    Something like SY or CY cable that actually had a low enough resistance braid to operate a large MCB would help with the snagging, but the flooding has no easy fix. If your genset has sockets for leads for unknown loads to plug into, it needs an electrode, an  NE bond and an RCD.

  • Yes, however in general those installations have equipotential bonding and fortuitous local earthing, so the effects are generally mitigated or limited

    Until you get to the outside tap or EV situation...

       - Andy.

  • Until you get to the outside tap or EV situation...

    At the moment, we only have evidence that this is genuinely problematic on a widespread basis for open-PEN situations, not particularly the situation you describe (it could be related to both frequency of occurrence and also the fact that effects of one are more readily noticeable than the other).

    Yes, there may be an elevated voltage in those situations, but there don't seem to be the same number or severity of instances as open-PEN. And even then I'm not aware of any deaths.

    However, compared with the "floating system with protective conductors connected to neutral point" ... whilst the damaged cable might appear to be rare, the consequences are very serious (and have happened) ... definitely a real problem with the possibility of instant death in a muddy field or on a wet construction site.

Reply
  • Until you get to the outside tap or EV situation...

    At the moment, we only have evidence that this is genuinely problematic on a widespread basis for open-PEN situations, not particularly the situation you describe (it could be related to both frequency of occurrence and also the fact that effects of one are more readily noticeable than the other).

    Yes, there may be an elevated voltage in those situations, but there don't seem to be the same number or severity of instances as open-PEN. And even then I'm not aware of any deaths.

    However, compared with the "floating system with protective conductors connected to neutral point" ... whilst the damaged cable might appear to be rare, the consequences are very serious (and have happened) ... definitely a real problem with the possibility of instant death in a muddy field or on a wet construction site.