Volt drop % - Private Supply Def

Good day everyone 

Public supply Volt drop 3% Lighting 5% Power.

Private supply Volt drop 5% Lighting 8% Power.

Define private supply?

Option 1 - HV public grid supply to privately owned transformer. Is LV supply private?

Option 2 - Main source of supply is from Privately owned source of generation such as PV, diesel/gas/nuclear generator?

Why is this not defined in BS7671?

Parents
  • Just a thought here. Is there any provision which specifies voltage drop at HV. Surely, if HV is low, Lv must also be low?

    No specific provision in BS 7671 ... and agreed, but transformers with tap-changers and AVC can be used to overcome that (or, in the LV system, autotransformers with tap-changers)

  • So just for clarity, your answer is both Option 1 & Option 2 will be considered private supply?

    Yes, they could both be considered a private supply, although as I have said the over-riding factors are not really the drop within the installation, but conformity with Regulations 525.1 and 525.201.

  • I’d go with Graham’s final conclusion. My opinion has been changed 

  • I have searched the web and found the definition of a private supply according to BS 7671.

    Why? Part 2 of BS 7671 contains the definitions within that standard?

    Also, what does "Wikipedia" define as a "source of energy" ?

    Wikipedia cannot interpret standards for us, I'm afraid.

    However, I could not find the exact location of this definition in the BS 7671

    I'm not sure it's there.

    If you take the diagrams in BS 7671 at face value, a transformer is a 'source of energy' which further supports the explanation I have given that a "private transformer" is a "private source of energy" - or, if you like, a private supply.

  • Option 1 is not a private supply, because it still relies on the public electricity supply system at the HV level.

    See my later response on "source". A transformer is a source (if you take the diagrams in BS 7671 at face value)

  • BS 7671 covers circuits supplied at nominal voltages up to and including 1000V AC or 1500V DC. It also applies to Extra Low Voltage (ELV) ranges and Low Voltage (LV) ranges, across a variety of frequencies.

    Thus oprion 1 is null and void!

  • Or more to the point, HV supply is not taken into account, thus transformer would be private supply 

  • Respectfully I disagree with your response. A private supply is defined as a supply that comes from a non-public source of energy, The HV supply is still a public source of energy, even if it is not considered. The transformer does not alter the source of energy, only the voltage level. Therefore, the transformer is not a private supply, but a public supply with a private transformer. 

  • The key thing about a private transformer - one where only you have the secondary side - usually the HV is shared with others (!) , is that you are free to set the taps (or call in the DNO to set the taps to your needs, depending on contract agreement and who has suitably qualified staff )

    This means that the voltage drop allowance normally reserved for the street cables is yours to play with - which if you have a large campus you will probably need to.

    Mike

    PS A private supply is defined as a supply that comes from a non-public source of energy, The HV supply is still a public source of energy, even if it is not considered.

    I think the authors of BS7671, and a number of designers of large sites do not agree with that interpretation.  :-)

  • fully agree with you. l

  • I think we need to distinguish between supply/ origin and source. 525.202 clearly states the volt drop measurement should origin of the installation (usually the supply terminals) and the socket outlet....

    BS7671 only applies to installations 1000v AC / 1500 DC and below. Thus it would deem the supply terminals on the LV side of the transformer as the oringin of the installation. If those terminals are privately owned, it would be considered a private supply.

    Annex 4 - 6.4, Table 4Ab - Voltage drop (ii) Low Voltage installation supplied from private LV supply.

    The HV supply or the source of energy is not considered for the purposes of Volt drop, but Origin of the LV supply is.

Reply
  • I think we need to distinguish between supply/ origin and source. 525.202 clearly states the volt drop measurement should origin of the installation (usually the supply terminals) and the socket outlet....

    BS7671 only applies to installations 1000v AC / 1500 DC and below. Thus it would deem the supply terminals on the LV side of the transformer as the oringin of the installation. If those terminals are privately owned, it would be considered a private supply.

    Annex 4 - 6.4, Table 4Ab - Voltage drop (ii) Low Voltage installation supplied from private LV supply.

    The HV supply or the source of energy is not considered for the purposes of Volt drop, but Origin of the LV supply is.

Children
  • If those terminals are privately owned, it would be considered a private supply.

    But the DNOs themselves were privatised after they took over from the old Electricity Boards - they may be regulated, provide a supply to the public, but their equipment isn't publicly owned.

       - Andy.

  • Much like the railways!

  • Thus it would deem the supply terminals on the LV side of the transformer as the oringin of the installation. If those terminals are privately owned, it would be considered a private supply.

    Agreed, although ownership is not the issue because the transformer could be leased, but still be private.

    It seems reasonable to regard the LV terminals of a private transformer as the origin, but otherwise it is the service head.

    The real point is whether the transformer supplies any other customer or not. So if it is just the one, it is possible to compensate for voltage drop within the installation. However if there is more than one customer, if the wick is turned up because of voltage drop in one installation, the voltage may be too high for another so there is less scope for adjustment.

  • Thumbsup

  • And whether or not the cable between the transformer secondary and your first load  or disboard is included in the sums or not.

    For a house in the street the volt drop sums start at the meter board, not at the transformer terminals, the voltage drop in the street mains is very real but it  "belongs" to the DNO - they only guarantee to hit somewhere between 208 to 253 at your cut out (and are usually quite well in, but not always)

    When you have a bit more control, you can usually do quite a bit better than that.

    Normally drop at HV can be neglected because the voltage  loss is scaled by the transformation ratio. (11kV/400 or whatever)

    Mike