When parts are not Exposed-conductive parts

BS7671

A mobile 19” racking enclosure containing a number of withdrawable LV class I items of equipment and other ELV measuring circuits contained within metal enclosures - the overall mobile racking unit is on wheels and floating from earth – however, the metal parts are only in contact with earth via the class I items located within it.

just considering protective systems and not EMC,  I would instinctively say that the entire mobile unit and its mechanical elements eg vertical struts, doors and outer enclosure form part of the ‘installation’ . All conductive parts which could become live under single fault of one of the class I items, so therfore all conductive  parts of the mobile unit ought to be bonded to its incoming supply earth terminal giving consideration to regulation 543.

But is it wrong to classify the racking system as exposed-conductive parts? Does the definition of exposed-conductive not extend to the racking it is bolted to?

Instead, does the racking qualify as extraneous-conductive parts which needs to comply with regulation 544 i.e. Bonded to the earthing terminal within the mobile enclosure with green/yellow not less than 6mm or half the CSA of the line conductors of the building’s incoming supply?

In summary, should I be bonding the racking parts via regulation 543, 544 or not bond at all?

Thanks

Parents
  • It depends if the rack is an appliance with one mains lead, or more like a set of shelves that happen to be metal, that kit is sitting on...

    In neither case is it exactly a fixed installation as per BS 7671 but the principles are similar. Does the rack include distribution -  a fixed 4 gang extension lead  for example? In your case a clear yes - you show a mini CU.

    If so good practice would be to earth the rack - and to be aware of earth leakage - if the whole rack is on one mains lead and the CPC failed how much total CPC current would be available to shock someone touching the rack ? If that is single fault to danger then provision for a secondary bond of the rack to supply earth may be needed,.

    Mike.

Reply
  • It depends if the rack is an appliance with one mains lead, or more like a set of shelves that happen to be metal, that kit is sitting on...

    In neither case is it exactly a fixed installation as per BS 7671 but the principles are similar. Does the rack include distribution -  a fixed 4 gang extension lead  for example? In your case a clear yes - you show a mini CU.

    If so good practice would be to earth the rack - and to be aware of earth leakage - if the whole rack is on one mains lead and the CPC failed how much total CPC current would be available to shock someone touching the rack ? If that is single fault to danger then provision for a secondary bond of the rack to supply earth may be needed,.

    Mike.

Children
  • It is the latter of several appliances that happen to be sitting on metal shelves - the complete mobile enclosure isn’t a product / appliance in its own right (well at least that’s my interpretation). 
    yes there will also be a multi-gang power distribution extension unit with IEC C13 type connectors

    ultimately the whole rack is fed from one supply inlet via a 6mm2 flexible cable with a 60309 plug. I don’t yet know what the earth leakage is, but my understanding around 543.7.1.202 is that my supply cable/connector is adequate. As for the internal equipment take your point and make sure these have secondary bonding if necessery - on a Sadie note, some class I devices have an earth stud on the rear panel  - is the purpose of these studs specifically for that leakage reason? Allowing a secondary bond or are they more EMC related?  

  • It is common to add earth studs of the back of kit that either has higher thna normal earth leakage, and needs additional high reliability CPC back to the supply, or to allow bonding to othe bits of kit as an earth loop mitigation.

    'Clean earths' are a bit of a misnomer, and really mean not sharing the CPC with something that is injecting large currents into the CPC, to ensure that there is not a large voltage difference between parts that are nominally earthed to the same thing, but not via  short route  to each other. It is very rarely the earth resistance that matters, but the micro-henry or so per metre that the wiring introduces  

    V=L*di/dt

    and all that.

    'The earth' voltage as a constant equipotential in space-time makes sense at 50Hz on an installations up to a some km across at least. The same idea does not extend well to microsecond pulses from motor  brushes etc.

    It is much better to consider 'earth'  more like a local 'level' but level like the deck of a ship - free to bob up and down relative to other decks on other boats  ( ie. an indeterminate and changing offset voltage relative to 'earth' in other equipment) or to the general land mass far away.

    Long earth leads are your mooring ropes, and the voltage gradient along them may slope up or down depending what is happening at each end.

    Mike.