When parts are not Exposed-conductive parts

BS7671

A mobile 19” racking enclosure containing a number of withdrawable LV class I items of equipment and other ELV measuring circuits contained within metal enclosures - the overall mobile racking unit is on wheels and floating from earth – however, the metal parts are only in contact with earth via the class I items located within it.

just considering protective systems and not EMC,  I would instinctively say that the entire mobile unit and its mechanical elements eg vertical struts, doors and outer enclosure form part of the ‘installation’ . All conductive parts which could become live under single fault of one of the class I items, so therfore all conductive  parts of the mobile unit ought to be bonded to its incoming supply earth terminal giving consideration to regulation 543.

But is it wrong to classify the racking system as exposed-conductive parts? Does the definition of exposed-conductive not extend to the racking it is bolted to?

Instead, does the racking qualify as extraneous-conductive parts which needs to comply with regulation 544 i.e. Bonded to the earthing terminal within the mobile enclosure with green/yellow not less than 6mm or half the CSA of the line conductors of the building’s incoming supply?

In summary, should I be bonding the racking parts via regulation 543, 544 or not bond at all?

Thanks

Parents
  • Will there be a UPS at the bottum of that rack?  How heavy are the PSUs?

    It is best practice to put the heavier kit at the buttom of the rack, it makes it more stable and less likely to topel over when someone slides any of the kit out and thus causing an imbalance.  The UPS (Uniturrupted Power Supply) will do several things.  Provide power for a set amount of time on power supply lose, clean the power coming into the unit.  Personally I always recommend a UPS on all racks.  The cost is an informed decission the customer has to make. 

    Back in the day when dealing with sound or comms equipment they would use smal length cables at the front of unit in yellow or yellow green connected to each peace of kit in the rack.  You would see then daisy chain from U1 to U47.  This was to help get rid of or disapate static it also helped to earth the cases of the kit should there be a fault .  These day people would call it some kind equipotential bonding.  If this was not done SOME kit would transfer that energy/static into the kit and cables.  This would result in hiss or static or crackle on the device like a phone or a speaker.  All of that bonding/Earth/equipotention stuff would then be connected to Earth.  Some people would call it a CLEAN EARTH.  Not sure how they cleaned it maybe with soap or something.  (poor humour)  Normally this Clean Earth got connected to a Earth rod and was separate for the rest of the instal Earth.  As a side not when you disconnect the power for this unit after it has been runnning for a while don't touch the Earth pin on the plug.  They get incredible hot due to intentional earth leakage of the DC equipment.  Another point to conside is the flooring, if it is carpet which will probably have a high nylon content it will build up staic as people walk over it you will then find engineers get staic shocks when the touch the metal kit or racking. 

  • Normally this Clean Earth got connected to a Earth rod and was separate for the rest of the instal Earth. 

    And the way many of those installations were carried out might now be considered unsafe - the "clean earth" system must be bonded to the mains Earth at least at one point, but there are other requirements in BS 7671 regarding the cpc needing to be installed to each point in wiring.

    These days, it's quire clear that Functional Earth (FE ... now coloured pink) has NO protective function.

    If the conductor is a combined protective and functional earth (CPFE) then it's green-and-yellow, and the requirements for protective earthing (PE) take precedence. BS EN 50310 (IEC 30129) contains an approach that is used to "clean up" the PE system so it's more suited for use by electronic systems, and separating sub-mains and final DBs for "noisy" and "victim" equipment is also recommended.

Reply
  • Normally this Clean Earth got connected to a Earth rod and was separate for the rest of the instal Earth. 

    And the way many of those installations were carried out might now be considered unsafe - the "clean earth" system must be bonded to the mains Earth at least at one point, but there are other requirements in BS 7671 regarding the cpc needing to be installed to each point in wiring.

    These days, it's quire clear that Functional Earth (FE ... now coloured pink) has NO protective function.

    If the conductor is a combined protective and functional earth (CPFE) then it's green-and-yellow, and the requirements for protective earthing (PE) take precedence. BS EN 50310 (IEC 30129) contains an approach that is used to "clean up" the PE system so it's more suited for use by electronic systems, and separating sub-mains and final DBs for "noisy" and "victim" equipment is also recommended.