Ipf result

Not sure what to record! 

All calibrated around the same time. Three readings taken on each instrument with swapped leads and probes all fairly consistent with photo.

Then move to a socket opened up using same leads;

Parents
  • Not sure what to record! 

    How about:

    a) <0.35 (tick)

    b) <1.1 (tick).(or even <1667 (tick)).

    After all the overall process is about showing the installation is safe, rather than being a box filling exercise and recognises the inherent variability in on-site measurement equipment.

    (slightly tongue in cheek perhaps)

       - Andy.

  • Appreciate what you are saying AJ, but it’s really just an academic exercise. I would like to understand just where the modern instruments go from being relatively accurate to total fruit machine. GN3 suggests around 0.1 ohm.

  • The value of 0.1 ohm given in GN3 may be a little optomistic, when you look at various manufacturers manuals.

    The manual for the Megger MFT1700 Series gives an operating range of 0.3 Ω to 1000 Ω for the high current loop test and 1 Ω to 1000 Ω for the low current loop test.

    Taking the Fluke 1620 Series as another example, the operating range is given as 0.2 Ω to 200 Ω for the high current loop test and 0.4 Ω to 2000 Ω for the low current loop test.

  • And given that all the meters use something around 10-20A for the high current test, and something equivalent to 1/1000 of that for the low current no trip tests, even with a lot of re-measuring and averaging it is not too surprising -  0.3 ohms it is looking for a voltage change of a few volts on 230V or so, and the low current  range is scrabbling about for some milli-volts.

    With the best will in the world there will be situations where the supply is not clean enough to allow that voltage change to be estimated reliably,

    The old analogue meters had the  possible advantage that you could see it was all squished up at the infinity end of the PSSC scale, and you knew not to trust it. A digital device gives you a very precise but slightly  different answer each time, but with no such caution to warn that  PSSCs of 3000A and  6000A are actually almost indistinguishable from infinite.

    Mike

Reply
  • And given that all the meters use something around 10-20A for the high current test, and something equivalent to 1/1000 of that for the low current no trip tests, even with a lot of re-measuring and averaging it is not too surprising -  0.3 ohms it is looking for a voltage change of a few volts on 230V or so, and the low current  range is scrabbling about for some milli-volts.

    With the best will in the world there will be situations where the supply is not clean enough to allow that voltage change to be estimated reliably,

    The old analogue meters had the  possible advantage that you could see it was all squished up at the infinity end of the PSSC scale, and you knew not to trust it. A digital device gives you a very precise but slightly  different answer each time, but with no such caution to warn that  PSSCs of 3000A and  6000A are actually almost indistinguishable from infinite.

    Mike