Ipf result

Not sure what to record! 

All calibrated around the same time. Three readings taken on each instrument with swapped leads and probes all fairly consistent with photo.

Then move to a socket opened up using same leads;

  • Get a set of decent leads from Kewtech to replace the Megger ones. Get a cotton bud and some switch cleaner and clean out the crud from the 4mm sockets on the back of the MFT and try again using the Kewtech leads on each instrument.

    Hope this helps and let me know how you get on?

    JP

  • Good spot. I was not familiar with the history of these type of testers, but apparently when they were launched in 2011, there were a few cases of confusing readings and then a firmware tweak, whatever that entails

    https://www.test-meter.co.uk/blog/megger-mft1700-series-overview-of-multifunction-installation-testers

    It may be interesting to compare firmware versions if that is possible,

    Also the official accuracy is (from here L-N/L-L tests ±5% ±5 digits

    Now it seems the spread observed is larger than that, but before rushing off, I'd be looking at the quality of the connections to the test leads - a very thin film of oxide on the banana plugs is all that is needed to add a handful of unwanted milli-ohms, When new these shrouded 4mm connections can  manage 0.5- 1milliohm per mated pair, but it rises with time as the condition of the mating surfaces deteriorates.

    Mike.

  • Now it seems the spread observed is larger than that, but before rushing off, I'd be looking at the quality of the connections to the test leads - a very thin film of oxide on the banana plugs is all that is needed to add a handful of unwanted milli-ohms, When new these shrouded 4mm connections can  manage 0.5- 1milliohm per mated pair, but it rises with time as the condition of the mating surfaces deteriorates.

    During my training, we were encouraged by one of the tutors to oscillate the plugs three or four times in order to abrade any corrosion. I have no idea whether it works or not.

    Notwithstanding annual calibrations, let's not forget the use of a check box or even monthly testing on a particular socket (in the workshop, kitchen, or office). If the plug connexion is deteriorating, it should be evident.

  • The value of 0.1 ohm given in GN3 may be a little optomistic, when you look at various manufacturers manuals.

    The manual for the Megger MFT1700 Series gives an operating range of 0.3 Ω to 1000 Ω for the high current loop test and 1 Ω to 1000 Ω for the low current loop test.

    Taking the Fluke 1620 Series as another example, the operating range is given as 0.2 Ω to 200 Ω for the high current loop test and 0.4 Ω to 2000 Ω for the low current loop test.

  • And given that all the meters use something around 10-20A for the high current test, and something equivalent to 1/1000 of that for the low current no trip tests, even with a lot of re-measuring and averaging it is not too surprising -  0.3 ohms it is looking for a voltage change of a few volts on 230V or so, and the low current  range is scrabbling about for some milli-volts.

    With the best will in the world there will be situations where the supply is not clean enough to allow that voltage change to be estimated reliably,

    The old analogue meters had the  possible advantage that you could see it was all squished up at the infinity end of the PSSC scale, and you knew not to trust it. A digital device gives you a very precise but slightly  different answer each time, but with no such caution to warn that  PSSCs of 3000A and  6000A are actually almost indistinguishable from infinite.

    Mike

  • Indeed Ross. So what does this reference to EN61557 mean in terms of function. Are we saying that any loop below 0.3 ohms might deliver unreliable results? At the lower loops, the instrument makes a simple ohms law calculation of Ipf which disregards the actual open circuit voltage and, of course, ignores the effect of reactance. 

    Ipf isnt really an issue in most installations using relatively modern equipment. 1000A + one way or the other is usually of no consequence. However, it does matter when we get to the Zs max for some high current MCCBs. It would seem to me that the MFT 1720 range is not the appropriate instrument when assessing such, but I always knew that.

  • The simple answer to the question 'Are we saying that any loop below 0.3 ohms might deliver unreliable results?' is yes.

    The instrument is capable of indicating values between 0.01 Ω to 1000 Ω but the accuracy of the indicated value can only be relied upon in within the range 0.3 Ω to 1000 Ω.

    The intrinsic accuracy is the accuracy expected under reference (laboratory) conditions whilst the maximum service error is the accuracy expected under actual (on-site) conditions.

    The intrinsic accuracy is often the only factor contributing to the maximum service error that you can easily quantify or control.

    At one time, manufacturers included information in their manuals showing how they calculated the maximum service error, taking into account factors such as ambient temperature, system voltage variation, system frequency variation and so on, but this doesn't seem to be as common now.

    I dont have access to the EN 61557 series of standards right now, but if I recall correctly, the maximum service error permitted for most measurements is ± 30 % of reading.

  • To quote Megger in their own booklet on loop testing:

    'As stated earlier in this booklet, we are not looking to venture into the physics of the testing, but suffice to say, when in close proximity of a transformer, the hand-held units available on the market today will struggle to return repeatable readings, when the calculated value is in the realms of milliohms and well below the stated range of the instrument'

  • It would be interesting to see if the readings are still varied with the new cable/leads and used on a calcard?

    https://calcards.co.uk/

  • It would be interesting to see if the readings are still varied

    The readings don't have to be the same between 3 instruments of the same model ... in fact it would be more unusual (although not wholly unknown) for the readings to be exactly the same.

    A Cal Card (or resistance box etc.) wouldn't be of much help in respect of low-Zs loop test either.