Final ring circuit - can they be simplified to loads in parallel with each other?

Am I correct in simplifying a ring circuit like this in theory? Assuming the loads are the same 1ohms and the distance between each load is the same as well.

Parents Reply Children
  • Well I was assuming that was a "thought experiment" by the original poster with easy numbers.
    After all 250 A is a bit much for the 2.5mm2 and the 32a breaker!  You probably get about 1/4 to 1/3 of a second before something lets go violently...

    And, If it does not, then the company fuse will do the honours after a few seconds.
    Mike.