Who is responsible for this lot

Hi guys

Found this on an EICR today. Serves 4 flats.  Massive holes in the top where the tails enter followed by main switches then very long runs in standard meter tails to each flat.   Is this the landlords responsibility or the supply company or parts each.   All in a locked cupboard in communal area with the key hooked at the top of the door for anyone to access

.   

Cheers Gary

Parents
  • Looks like an insulted version of a Bemco unit. Just out of curiosity, how close are bare live parts to the holes? IIRC the requirement is IP4X or IPXXD - the latter is somewhat more lax - as long as a 100mm long 1mm dia wire can't touch live parts, it could well comply technically.

       - Andy.

  • The terminals i could see were a fair way down.  Do these sort of things generally have fuses in ? or do i have a load of unfused meter tails Slight smile

  • Unless there is an obvious service head somewhere else - cant see on this one,

    There will be a row of 100A fuses that belong to the DNO in the white box, probably a few per phase. Does it have anti tamper seals and how is your attitude for risk....

    I may be tempted to go a little  wild with a mastic gun and split some universal grommets, assuming the holes are a standard size and 32mm.

    https://www.tlc-direct.co.uk/Products/GR32B.html

    and then get out and not ask too many questions.

    M.

  • Cheers Mike.   I can't get access again now without going through the estate agent. I'll just put it in the report and leave it to them to sort out if it needs it.  Thank you all for your help.  

    Gary