Code for a concentric cable on domestic EICR ?

Hi guys.  How would you code a Concentric cable feeding a detached domestic garage.  Cable is i believe a short run under a tarmac drive although i can't find the house connection ( probably behind kitchen cupboards ). There is plenty wrong with how it has been connected but specifically the use of the cable. I was thinking a C3 as i don't think it's dangerous as unlikely to be damaged in the ground because of the tarmac.  Any thoughts please.  

Thanks Gary

Parents
  •  The whole install is a mess. 

  • I'm struggling to make out the details on that picture - but the white strand sticking up between the strands used as N and those used as a c.p.c. suggests it might be an (older) version of split-con with all outer strands bare and just an insulating spacer between those used for N and those used for PE (newer versions tended to have individual 'insulation' on the N strands instead (well more of a plastic covering, not necessarily up to proper insulation standards)). With that type I think it was conventional to sleeve the N strands for termination, but if it was inside an enclosure, it's probably not an absolute requirement.

    If it is split-con, while it doesn't meet today's specs, it'll act just as well as an armoured cable if struck by a digging too - provided the N really is close to Earth potential. Likewise the lack of proper insulation on the N part of the outer (just a sheath), doesn't fully comply with today's words, the actual risks will be minimal provided N remains close to Earth. Hence the earlier question about the reliability of the upstream N connections. Solid bolted connections all the way (like a c.p.c.) would be good, DP switching (or MCBs etc) including the N less so, as there likelihood of a contact failing, leaving the N open and L connected, increases; SP switching (or fuses or MCB) in the N alone would of course be right out.

      - Andy.

  • Unless they are heavily oxidised, it looks to me like the N strands have a thin layer of black insulation on them.

Reply Children
No Data