EIC or MWC

Scenario:

Existing lighting circuits with fluorescent luminaires upgraded to LED equivalents.

Circuit breaker changing type and/or rating.

Contractor has provided an MWC covering the works.

All looks good, but because the circuit protective device is not strictly a like for like change, should they have actually provided an EIC?

Parents
  • Like, others, I do not think that the exact paperwork matters, but why was the rating of the breaker changed please?

    This begs a further question - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

Reply
  • Like, others, I do not think that the exact paperwork matters, but why was the rating of the breaker changed please?

    This begs a further question - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

Children
  • - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

    - in terms of the process to follow or the work done, no. In terms of the tests needed, no.

    In terms of if the design calcs for the circuit needing to be redone, maybe, and in turn that may affect the test limits.

    So, again, is the information given adequate and appropriate ?

    The type of form  is irrelevant   that could be a house special, unless defined by contract.

    Mike.

  • Worth considering if they changed a MCB to a RCBO (preferably Dual pole)

    58w fluorescent luminaires changed to 12W versions

    Inrush current of LED may require the use of a C curve breaker rather than a B

    B30 changed to a B20 or B16

  • Yes, that was not quite what I meant. I wondered whether it made any difference to the paperwork. MEIWC (page 513 of the BBB): "Part 1 3. Description of the minor works ....." Insert something like, "Fluorescent luminaires changed to LED. Overcurrent protective device changed." The value(s) of the new device will be specified in Part 3.