EIC or MWC

Scenario:

Existing lighting circuits with fluorescent luminaires upgraded to LED equivalents.

Circuit breaker changing type and/or rating.

Contractor has provided an MWC covering the works.

All looks good, but because the circuit protective device is not strictly a like for like change, should they have actually provided an EIC?

Parents
  • Like, others, I do not think that the exact paperwork matters, but why was the rating of the breaker changed please?

    This begs a further question - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

  • - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

    - in terms of the process to follow or the work done, no. In terms of the tests needed, no.

    In terms of if the design calcs for the circuit needing to be redone, maybe, and in turn that may affect the test limits.

    So, again, is the information given adequate and appropriate ?

    The type of form  is irrelevant   that could be a house special, unless defined by contract.

    Mike.

Reply
  • - is there any difference between replacing an MCB, like for like, as opposed to changing for a different rating?

    - in terms of the process to follow or the work done, no. In terms of the tests needed, no.

    In terms of if the design calcs for the circuit needing to be redone, maybe, and in turn that may affect the test limits.

    So, again, is the information given adequate and appropriate ?

    The type of form  is irrelevant   that could be a house special, unless defined by contract.

    Mike.