Bonding of a bolted-together equipment rack located in a vehicle

I have a custom built stainless steel equipment rack that is made up of many individual sections of stainless steel angle that are bolted together to form the complete rack. The stainless steel parts will not have any paint or finish applied. 

The equipment rack will be mounted in a vehicle with the bottom sections of the rack bolted to the metal floor of the vehicle. 

The equipment rack will have 12 Volt and 28 Volt equipment mounted on it.

My question.....

- Does a single wire connection from the vehicle's Main Earth Terminal (MET) to the equipment rack meet the protective bonding requirements?

I am hoping that I do not need to have a separate wire from the MET to each individual piece of steel angle, or a 'strap' linking the bolted-joints.


  •   

    It depends if a ground wire is run to the equipment of if it is grounded through the steel rack.

    If you put steel storage racking in the back of your van you would not bond it, if you were to screw a DC 12 V Makita cordless  battery charger into the rack you would only have to run one conductor to it from the vehicle fuse board or wherever you get the supply from, the other conductor can simply be grounded to the rack or the vehicle body, so long as there’s continuity, I cannot imagine many people are going to “bond” the rack as such.

    If the vehicle was live at 230 volts you are inside a Faraday cage formed by the bodywork, you would be fine until you tried to get out and put a foot onto the ground outside of the vehicle.

    If the rack is inside the Faraday Cage and not extraneous, is there going to be an issue?

    If you are in a vehicle that is caught up in electric cables, DO NOT TRY TO GET OUT!

    www.fwi.co.uk/.../cool-headed-tractor-driver-unharmed-power-cable-smash

  • That Farmers Weekly article is behind a paywall, you may be able to read it if you don’t have any cookies on your device.

    A different story:

    Unbeknown to him, the trailer had touched the power line and, as he got out of the tractor cab, stepping on to the ground and holding the metal door, 11,000 volts of electricity shot through him.

    www.farminguk.com/.../farmers-told-to-take-care-around-overhead-power-lines-as-harvest-approaches_49528.html

  • Nevertheless a conductor required for grounding is not bonding.

  • Which is actually what i have been saying.

  • Hi Mike,

    Good points.

    I think an isolation transformer would be sensible too. Our maximum load is only 3500 Wattts, so transformer size won't be ridiculous.

    I appreciate this doesn't guarantee safety.

    Regards, 

    Steve

    Steve

  • We will definitely be following the manufacturer’s recommendations, and we shall also be employing an electrician to inspect the complete installation. 

    Regards,

    Steve

  • An isolation transformer may be a consideration for a single piece of equipment,  but not an installation supplying two or more. 

    The first AC 230 V fault to the rack and vehicle metalwork is not noticeable, the second causes problems.

    www.google.com/url

    Edit- it’s not impossible to use IT earthing, but 717.411.6.2 or 717.413 applies and you cannot simply buy a blue portable power tool transformer to use.

  • An isolation transformer may be a consideration for a single piece of equipment,  but not an installation supplying two or more. 

    An isolation transformer can be used for things other than separation - creating a local TN-S system where "T" is the chassis rather than the planet for example - you can then have ADS even if the supply PE is faulty or inadequate and it's much more difficult to get hazardous voltages between vehicle and  ground outside. (e.g. fig 717.6 in BS 7671 section 717).

    Separated system feeding two or more items for current-using equipment (oddly class I accessories don't seem to count) are permitted if you have skilled or instructed person about - in that case you'd have all the exposed-conductive-parts connected together by a protective conductor - so a 2nd fault (from a different line) causes a short-circuit (ADS style) which should cause disconnection.

       - Andy.