Trimble high Zs
Hi all, I’m new to cable calculation software and I’m having some trouble with Trimble. I’m sure it must be a settings issue, but when calculating for a circuit I’m getting much higher than expected values for Zs and in particular, Z2.
If I incorporate the CPC within a multicore cable I get results similar to that calculated by hand, but when I have a separate CPC the values end up way off and I have high Zs errors.
Please help!
  • Hi, I don’t use Trimble but could it be due to the software applying PD IEC/TR 50480:2011 to the calculations?
  • I’m getting much higher than expected values for Zs and in particular, Z2.
    Are these armoured cables? If so, your "by hand" calculations should also lead to a higher value (in the way that AMK said) as discussed in the IET Electrical Installation Design Guide.