240v outdoor plugs/socket regs or guidance for industrial work areas

Can someone point me in the direction of regs or good guidance relating to outdoor use of a 16a commando type socket vs 13a standard outdoor domestic socket in an outdoor industrial setting. We have an electrician who is arguing that because of rcd protection the 16a blue sockets are overkill. My view is the 13a plugs/sockets are dangerous in the wet - where the socket has little ip rating once the cover is opened. I’m struggling to find good guidance that supports my arguments.

Parents
  • 13A sockets are not really the right object if they are going to be splashed or handled by folk with wet hands - to rely on the RCD implies that you accept tripping, and perhaps quite painful shock while it trips, as the 'normal'  safety regime.  Outdoors means different things - a socket in a car port or under an awning my be OK, and fair weather only applications (the gardener never cuts the grass in a storm..) 13A may be all right.  Equally an extension lead in a puddle at a car wash certainly isn't.

    BS7909 may be worth a look - not industrial of course, but camps and pop festivals are certainly examples of outdoors and all weather situations.

    https://www.hse.gov.uk/electricity/precautions.htm

    In wet surroundings, unsuitable equipment can become live and make its surroundings live too. Fuses, circuit-breakers and other devices must be correctly rated for the circuit they protect. Isolators and fuse-box cases should be kept closed and, if possible, locked.

    Cables, plugs, sockets and fittings must be robust enough and adequately protected for the working environment. Ensure that machinery has an accessible switch or isolator to cut off the power quickly in an emergency.

    Not black and white, but not '13A is always OK' either.

    Mike

Reply
  • 13A sockets are not really the right object if they are going to be splashed or handled by folk with wet hands - to rely on the RCD implies that you accept tripping, and perhaps quite painful shock while it trips, as the 'normal'  safety regime.  Outdoors means different things - a socket in a car port or under an awning my be OK, and fair weather only applications (the gardener never cuts the grass in a storm..) 13A may be all right.  Equally an extension lead in a puddle at a car wash certainly isn't.

    BS7909 may be worth a look - not industrial of course, but camps and pop festivals are certainly examples of outdoors and all weather situations.

    https://www.hse.gov.uk/electricity/precautions.htm

    In wet surroundings, unsuitable equipment can become live and make its surroundings live too. Fuses, circuit-breakers and other devices must be correctly rated for the circuit they protect. Isolators and fuse-box cases should be kept closed and, if possible, locked.

    Cables, plugs, sockets and fittings must be robust enough and adequately protected for the working environment. Ensure that machinery has an accessible switch or isolator to cut off the power quickly in an emergency.

    Not black and white, but not '13A is always OK' either.

    Mike