So I'm trying to work out some cable calcs for a sub main leaving LV Side distribution equipment sited adjacent to a 800Kva transformer , any ideas what the Ze is likely to be ? I would think it will be really low
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
So I'm trying to work out some cable calcs for a sub main leaving LV Side distribution equipment sited adjacent to a 800Kva transformer , any ideas what the Ze is likely to be ? I would think it will be really low
0.02 would be a bit high - at full load a drop of 1200 A*0.020hm= 24 volts circa 10% - I'd expect half that or less for the impedance right on the terminals.
Mike
Thanks for the explanation, much appreciated