Expected Ze reading on LV adjacent to a 800Kva transformer ?

So I'm trying to work out some cable calcs for a sub main leaving LV Side distribution equipment sited adjacent to a 800Kva transformer , any ideas what the Ze is likely to be  ? I would think it will be really low 

Parents
  • 0.02 Ohms

  • 0.02 would be a bit high - at full load a drop of 1200 A*0.020hm= 24 volts circa 10% - I'd expect  half that or less for the impedance right on the terminals.

    Mike

  • Thanks for the explanation, much appreciated 