Touch voltage

Hello

I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


Parents
  • Hmm, well defined this way Ut - the 'touch voltage' is between the case of the faulty kit, and the exposed part - here the vertical pole at the right hand image edge.
    We seem to neglect any resistance and voltage drop between the point of touch on the pole  and the MET and as only a modest current flows in the victim that is OK,
    They give us a voltage, 57volts, so we know the current in the R2 (half ohm). (have R have V, - get I. ) Now both the substation and the house have electrodes connecting to the soil around them with a non-zero impedance, so if current is flowing in the ground, then the MET will not be at zero volts relative to terra-firma earth potential - an electrode far away if you like- but that is not what is being touched.

    Mike.

  • Thank you , just to confirm the three sketches are mine , and I have added figures