Touch voltage

Hello

I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


  • Hmm, well defined this way Ut - the 'touch voltage' is between the case of the faulty kit, and the exposed part - here the vertical pole at the right hand image edge.
    We seem to neglect any resistance and voltage drop between the point of touch on the pole  and the MET and as only a modest current flows in the victim that is OK,
    They give us a voltage, 57volts, so we know the current in the R2 (half ohm). (have R have V, - get I. ) Now both the substation and the house have electrodes connecting to the soil around them with a non-zero impedance, so if current is flowing in the ground, then the MET will not be at zero volts relative to terra-firma earth potential - an electrode far away if you like- but that is not what is being touched.

    Mike.

  • Thank you , just to confirm the three sketches are mine , and I have added figures

  • I think what you are missing is that - with bonding in place - you are using the pipe to touch two points on the same conductor; not a live point and earth.

  • We have a fault and at the Exposed CP we have a voltage of say 115V

    OK (or using the example, which includes a factor for a possible increase in supply voltage of up to 10%, 126.5V).


    The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

    Not according to the resistances in the left hand diagram. With the system earth reference at the source, there's Ze (of 0.35Ω in this example, half in L and half in the PEN) to take into account - so with an overall loop resistance of 1.35Ω (0.35+0.5+0.5)  and so 0.675Ω (0.175+0.5) between true Earth and the fault, the c.p.c. (between MET and exposed-conductive-part) accounts for 0.5Ω of that - so closer to three quarters rather than half.

    But since the MET will be at a raised potential It can't be to earth?

    Correct the MET will not be at true Earth potential (the 0V of the general mass of the earth) - so without bonding, the extraneous-conductive-part may remain at true Earth potential so you get the full 115V (or with Cmax 126V) between the faulty exposed-conductive-part (appliance) and the extraneous-conductive-part (pipe).

        - Andy.

  • The touch voltage calculated assumes the person subject to it is standing on a floor that is remote from earth, as would be the case inside most normal buildings. The value is the product of the fault current and the resistance of that part of the earth path from the fault to the DNO transformer when no main protective is in place or just the voltage drop along R2 when it is in place. In TN systems with low values of resistance in the earth path back to the transformer, the effect of main protective bonding will be relatively small in reducing touch voltage, but is crucial in TT systems where without MPB, the touch voltage could be close to the full fat system voltage to earth.



  • Thank you very much, thats really helpful. Could I please ask a bit more.

    I have re drawn it,  (3) But I am still unsure about what the potential difference will be between EXP and EXT parts
    I make it 33V so I must be doing something wrong.

    I think what you are missing is that - with bonding in place - you are using the pipe to touch two points on the same conductor; not a live point and earth.

    Not quite following that. Are you saying as in drawing 5 the EXP and EXT will be the same potential?  I understand they are now connected together, so does that reduce the original 

    In drawing 6 I have also added a supplementary bond, but I am unsure how to calculate its effect.

  • In drawing 6 I have also added a supplementary bond, but I am unsure how to calculate its effect.

    In diagram 6, you have to calculate the share of current in the SB and mutiply by its resistance to get the touch voltage because -

    a person touching the exposed-c-p and extraneous-c-p is actually just touching the ends of the SB in the current path SB and pipe to MB connection.

    Also your resistance values are rather high which is skewing the results.

    For example a 10m SB of 4mm² is only 46mΩ (0.046Ω)

  • Yes , you are right. Its not really realistic, I was just thinking of the Maximum it could be i.e  R≤ 50/200 0.25.

    Thank you

  • I make it 33V so I must be doing something wrong.

    I reckon the MET will be at about 33V (187A * Zpen) - and the p.d. between the MET and the exposed conductive part will be 93.5V (187A * 0.5Ω) - making the voltage (above true earth) of the exposed-conductive-part 126.5V.

        - Andy.

  • In drawing 6 I have also added a supplementary bond, but I am unsure how to calculate its effect.

    You might need to make some assumptions. If you assume the pipework has negligible resistance, then the supplementary bond is in effect parallel with the c.p.c - which reduces the overall earth fault loop impedance, and so increases the fault current. Then it's pretty much the same procedure as before (if with different numbers).

       - Andy.