I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


Parents


  • I think I have it now as in the first 2 pics

    In the 3rd I have tried to calculate touch voltage with supplementary bonding in place.
    Im I in the right area?

    Thanks very much

  • Im I in the right area?

    More or less, except that -

    the Zs will be reduced by the SB being fitted, and 

    not quite all of the fault current will flow through the SB; a (small) part of it will flow through R2.

    So Ut = If (in SB) x 0.05

Reply
  • Im I in the right area?

    More or less, except that -

    the Zs will be reduced by the SB being fitted, and 

    not quite all of the fault current will flow through the SB; a (small) part of it will flow through R2.

    So Ut = If (in SB) x 0.05