Modernising a Domestic Installation - Multiple Consumer Units
I'm buying a house where the electrical installation is, for want of a better description, a complete mess!
I'm assuming that the existing supply is PME and will check and also measure earth the loop impedance when I get full access.
Currently there's one consumer unit in the downstairs entrance which is old having only fuses and no spare ways.
The plan is to start by renovating upstairs, which will involve re-insulation and will provide great access..
So I think I may as well re-wire upstairs while access is available.
I reckon that the easiest thing to do will be to install an upstairs consumer unit, and at some later time, a new downstairs one.
This will also allow for shorter final circuit cable runs so simplify installation.
Hence to my current deliberations.  I think the following is correct.
(a) The 'main distribution board' needs to house CBs only to protect the cables to the CUs.  (CUs will include RCDs whether required or not)
(b) There's no requirement to have any RCDs in the 'main distribution board'.
(c) There may be merit - or even a requirement - to include SPDs in which case these would best be in the 'main distribution board'.
Does this make sense?  Any comments appreciated.
For background: in my early career I worked as an electrical building services designer for a consultancy.  That was a a long time ago, and that work was on commercial not domestic premises.
  • (a) Yes, but they may not discriminate well with the final circuit MCBs, so if a 32 A MCB trips, it is likely to take a 63 A MCB protecting the distribution circuit with it. This may be an acceptable risk. Fuses are an alternative option.
    (b) Agreed.
    (c) Yes, or adjacent to it.
  • Thanks for your response, Chris.
    (a) Yes, I certainly need to look at discrimination since if faults were tripping a 63A MCB and the whole CU, that would be a nuisance.  Would rather avoid fuses though.  Perhaps non-B characteristic MCBs would be an option here.
    (c) My interpretation is that use of a SPD would not be mandatory, so I suppose I need to consider the merits or otherwise of this.  We don't get much in the way of lightening around here, and no hefty surge-inducing loads are expected.
  • I think the answer to (b) will depend on what sort of cables you use, and where they are run.
  • Hi John
    Unless you have wooden floors down stairs that can be lifted to wire the ground floor sockets pretty much all of the wiring for up and down stairs is in the ground floor ceiling / first floor floor. If this is the access you are talking about you will need to at least partially rewire or install cables for down stairs at the same time. Certainly the ground floor lights will be in the ceiling.  I personally think an upstairs CU over complicates things unless this is a very large installation.
    Gary
  • Downstairs floors are wooden, and so I think that cabling to sockets will be underfloor but will only know that for sure when I start to pull things apart.
    I've seen some evidence of steel conduit, so hopefully if this is in place, running replacement wires will be easy.  Probably won't be that lucky!
    It's not a huge installation, but access to the downstairs CU is problematic and I want to get to the stage where the existing cupboard contains only the distributor's equipment.  The use of two CUs is very much for convenience of doing work but I will have more circuits than is perhaps common.
  • I've not decided on the cable yet, but I don't think it would need to be bigger than 25sq.mm conductor size.  Might get away with 16sq.mm.
    The lengths are under 8m so not too expensive simply to use SWA three core.
  • (c) In my own home, I decided to install SPD, largely on the basis of discussions in this forum. Like you, we see very little lightning and I do not have much vulnerable equipment. Nothing has been damaged during the past 27 years that we have lived here. It was not exactly expensive, but if installed in the CU it takes up 3 ways as opposed to 1 if adjacent.
    (a) Yes, you may be able to fit a type C in the first DB. In my own installation, the distribution circuit is about 35 m long, so if a fault occurs a few metres downstream of the second DB, there will probably be discrimination.
    The important point is, despite any of the theoretical concerns, I cannot remember when an MCB last tripped. It is not an everyday risk!
  • The 'main distribution board' needs to house CBs only to protect the cables to the CUs.  (CUs will include RCDs whether required or not)
    As above, consider the type of cables for the submains - if ordinary insulated & sheathed and concealed in a wall it'll likely need 30mA RCD protection - hence with no discrimination with downstream RCDs. SWA avoids that problem, but isn't easy to run neatly or rear-entry to a CU in a domestic setup where aesthetics tend to be demanding.
    My preference is for HBC fuses for submains - better for discrimination and with most designs you get terminals designed for larger conductors, rather than the usual MCB style shallow cage clamps which don't always do well with large stiff 7-strand.
  • Thanks, Andy
    I've been looking at sub-main cabling options. I think the best option is probably SWA.
    Should be able to run this down from the 'main distribution board' to underfloor and then up to the CUs which will be in cupboards, so I don't mind SWA cables coming in the bottom.  Avoids the need for mechanical protection although I'll need to look at ratings where this will be in a wall behind plasterboard.
    Also, I think if I use 3-conductor SWA then I don't need to run any additional separate earths to the CUs.  I do need to check that point though.
    Discrimination is an issue, so don't want RCDs in the 'main distribution board' (except if I decide to take a garage feed from there).  Like the idea of the HRC fuses, but will need to check the loop impedance to work out whether there could be enough fault current for correct operation of these.
    If you have one, I'd quite like a recommendation for which manufacturer's products to look at, particularly for the 'main distribution board'.
    John
  • Like the idea of the HRC fuses, but will need to check the loop impedance to work out whether there could be enough fault current for correct operation of these.
    Rough rule of thumb (making all sorts of semi justifiable assumptions like N and PE have the same impedance etc) - if voltage drop is OK then a fuse (5s disconnection time) or a C-type MCB are likely to be OK for Zs. Certainly do the maths to be sure. but if generally if Zs is an issue, v.d. is going to be a bigger one.
    Ah, now you're asking. The lack of an affordable mult-way fuse based DB for domestic use has been debated on here a few times. Single way units (e.g https://www.tlc-direct.co.uk/Products/WYDSF100M.html or even cheaper variants) are readily available but no-one seems to do multiway versions. (You can go for a industrial or Ryefield type unit, but rapidly get into silly money for a limited domestic setup). Some of us have resorted to DIN rail mounted 58x22 fuse holders, a switch disconnector, MCB sized DIN rail terminals for N and an assortment of bits of bus-bar in a suitable enclosure for our own home use ... but recent regulation tightening has made that a little more awkward to justify.  I guess the official answer is a few of the 1-way units, Henley blocks and an upstream switch disconnector (e.g. REC2) if the DNO hasn't already provided one. Simple enough and I suppose easy to maintain but not particularly neat.