Import and Export meter overloading - is it possible?

I had a large electricity supplier install solar PV and battery system and the import meter melted followed by the export meter.

They are stating that it is my issue and not there's as I have overloaded my consumer unit.

The import meter was rated to 100A

The export meter was rated to 100A

My incomer is protected by an 80A fuse

My export meter is on a supply protected by a 50A MCB

They are saying it is not their issue and I will have to go through the Ombudsman if I don't agree with their report.

How do I deal with a large company that refuses to take responsibility for faulty workmanship.

   

Parents Reply Children
  • Maximum power drawn for the year is 15.8kW during winter with heating on, batteries charging and EV charging.

    Was all of that through the 50 A circuit?

    Regardless, if it's "overloaded" surely the design should conform to BS 7671, and hence arranged or protected so that overload is not likely?

    How much s it worth to fight? i.e. what is the possible benefit, and what has been lost. Balance the tw

    Agreed ... the sad thing is that it might cost more to get legal and technical experts involved, than it costs to repair the installation (and if appropriate correct any defects).

  • Import meter on 80A main fuse - blue wire

    Export meter on 50A MCB - brown wire

  • Import meter on 80A main fuse - blue wire

    Export meter on 50A MCB - brown wire

    That alone doesn't tell us where the current was flowing at any given points in time unfortunately.

    However, a line conductor on one meter and neutral on the other does (without seeing the installation) make it appear that overload may have occurred (but without seeing further evidence, it's not conclusive).

    As others have said, there are also a number of things that could cause this issue other than "overload" also - faulty equipment, or terminal not tightened to manufacturer's recommended torque (too tight or not tight enough), as well as other thermal considerations ... without seeing more evidence, it's not possible to do anything other than speculate.

  • The graph at the top shows total current drawn.

    The garage is on a 50A breaker and has normal garage equipment plus the solar batteries and invertor