What is the classification code on an EICR for Solar PV installed on one side of a split load RCD consumer unit?
What is the classification code on an EICR for Solar PV installed on one side of a split load RCD consumer unit?
What is the level of danger you think this poses ? - that will depend what else is on that RCD, and perhaps on the power level and installation method of the PV inverter.
Are other things wrong? - Are the isolators and so forth suitable, is the overload protection appropriate etc.
Are there also batteries as part of the installation ?
Mike
What is the level of danger you think this poses ? - that will depend what else is on that RCD, and perhaps on the power level and installation method of the PV inverter.
Are other things wrong? - Are the isolators and so forth suitable, is the overload protection appropriate etc.
Are there also batteries as part of the installation ?
Mike
Are you thinking along the lines of DC currents present and masking fault currents, preventing the RCD from operating?
If the inverter is capable of DC feedback