What is the classification code on an EICR for Solar PV installed on one side of a split load RCD consumer unit?
What is the classification code on an EICR for Solar PV installed on one side of a split load RCD consumer unit?
What is the level of danger you think this poses ? - that will depend what else is on that RCD, and perhaps on the power level and installation method of the PV inverter.
Are other things wrong? - Are the isolators and so forth suitable, is the overload protection appropriate etc.
Are there also batteries as part of the installation ?
Mike
Are you thinking along the lines of DC currents present and masking fault currents, preventing the RCD from operating?
Are you thinking along the lines of DC currents present and masking fault currents, preventing the RCD from operating?
If the inverter is capable of DC feedback