Light fitting and insulation

The fitting below was discovered during a representative inspection of a dwelling in an estate of over 100 units. There are over 1000 of these fittings, all covered in at least one layer of glass wool type thermal insulation.

One might wonder how the warning label was missed, or perhaps ignored, so very many times. There are also issues with achieving 30min modified fire resistance for the first floor. The one in the photo is in a bathroom. The contractor smugly  defended the absence of an IP rating as the fitting was installed at a height of 2.7m, well outside the designated zones in 701. I hear this sort of comment all the time. Perhaps if guys were better tutored on Chapter 13, a more holistic attitude to design might prevail.

Parents
  • Is the primary concern the lack of fire-rated downlights with rooms above (527.1.2)

  •  

    Is the primary concern the lack of fire-rated downlights with rooms above (527.1.2)

    That regulation is a bit of a catch-all but it has to be considered in terms of what the Building Regulations require. For a two storey dwelling, the first floor needs to have a fire resistance of 30/15/15 REI (sometimes referred to as 30minute modified). Where certain minimum parameters are met for each element of the floor construction, downlights with a specific fire rating may not be required. That is not to say that benefit would not be had by installing them.

    See Appendix C Best Practice Guide 5 issued by Electrical Safety First. In this case the floor construction is much more than those parameters demand.

  • But considering fire barriers, sealing arrangements, and protection against thermal effects, the absence of fire hoods on open-back downlights would not comply with regulations 537.1.2. 

  • I take it you mean 527.1.2 which refers to "wiring systems". A luminaire would not be part of a wiring system.

    I am not being argumentative. I acknowledge that 7671 and, indeed, the Building Regulations, provide for minimum standards which can be augmented at the discretion of the person applying them. However, I must return a report that is technically correct with regards to the requirements of the standards being quoted in it rather than being prejudiced to individual preference. 

  • Sorry, yes 527.1.2.

    I understand that you are not being argumentative, and I am here to assist as best as I can. In my experience, I have consistently referred to Regulation 527.1.2 when conducting EICRs for installations where ceiling fire barriers are penetrated by downlighters, particularly if there are rooms above. 

Reply
  • Sorry, yes 527.1.2.

    I understand that you are not being argumentative, and I am here to assist as best as I can. In my experience, I have consistently referred to Regulation 527.1.2 when conducting EICRs for installations where ceiling fire barriers are penetrated by downlighters, particularly if there are rooms above. 