What's everyone's views on ELV cables contained within the same pvc conduit as LV . I believe it to be ok if all the cables are insulated to the highest voltage. Not sure I would say it was good practice and not sure about colour coding
What's everyone's views on ELV cables contained within the same pvc conduit as LV . I believe it to be ok if all the cables are insulated to the highest voltage. Not sure I would say it was good practice and not sure about colour coding
Hi, I agree it’s ok. BS 7671Table 51, which pertains to the identification of conductors, and the methodology you outlined are addressed in Regulation 527.1
- Andrew
Hi, I agree it’s ok. BS 7671Table 51, which pertains to the identification of conductors, and the methodology you outlined are addressed in Regulation 527.1
- Andrew