Mixing LV and ELV Cables in the same conduit

What's everyone's views on ELV cables contained within the same pvc conduit as LV . I believe it to be ok if all the cables are insulated to the highest voltage. Not sure I would say it was good practice and not sure about colour coding

Parents
  • Hi, I agree it’s ok. BS 7671Table 51, which pertains to the identification of conductors, and the methodology you outlined are addressed in Regulation 527.1

    - Andrew

Reply
  • Hi, I agree it’s ok. BS 7671Table 51, which pertains to the identification of conductors, and the methodology you outlined are addressed in Regulation 527.1

    - Andrew