What's everyone's views on ELV cables contained within the same pvc conduit as LV . I believe it to be ok if all the cables are insulated to the highest voltage. Not sure I would say it was good practice and not sure about colour coding
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
What's everyone's views on ELV cables contained within the same pvc conduit as LV . I believe it to be ok if all the cables are insulated to the highest voltage. Not sure I would say it was good practice and not sure about colour coding
I believe it to be ok if all the cables are insulated to the highest voltage.
And the EMC requirements are met where appropriate (Section 444 of BS 7671)
I believe it to be ok if all the cables are insulated to the highest voltage.
And the EMC requirements are met where appropriate (Section 444 of BS 7671)