DNO Residential Supply Main Cutout Fuses and Potential Fault Current (PFC)
There seems to be a lot of emphasis on recording the highest value of PFC being less than the protective devises can safely handle, but little or no reference to when the pfc might be too low to operate the device in the prescribed time. In fact, most installation and inspection certificates simple note the device manufacturers maximum safe fault current, giving the electrician an excuse perhaps to not even measure the pfc!
I’m long retired but investigating a potentially serious electrical fire for a friend, though fortunately, this time, no fatalities as it was confined to a detached intake cabinet well away from the building. Which brings me to another point, the ESQC Regulations stress reporting an incident to the Secretary of State if any fatalities, but no such requirement if none (this time!). Sadly, a missed opportunity perhaps to reduce the risk of similar failures causing fatalities in future.
Anyway, for now, back to the pfc issue: In their case they had very recently had a 3 phase upgrade to their large property, with DNO 100amp cutout fuses (BS1361 or similar). The supply service cable serves several properties, with theirs being near the end of the supply service cable. Both the calculated pfc and measured value indicate around half the pfc required to operate the cutout fuses in the prescribed time, and in the event, persisted in the fault mode (apparently faulty meter or loose meter connection) for perhaps in excess of 15 minutes, further aiding the developing fire. Currently, their loads are all single phase and shared across the 3 phases, with ample capacity for future load additions.
So 2 questions if I may, one around the related ESQC regulations notification issue, and one about no obvious provision for recording a measured value of pfc on certificates, and no obvious requirement on the certificate to act accordingly when the measured pfc is too low.
  • After the fire, the DNO contractor joined in a short section replacement running up to the customer intake cabinet, apparently smoke heat/damage precaution. The G/Y goes back to where they added the 3 phase upgrade joint, and earth rod.
  •   I meant to add a photo earlier of the post fire replacement cabinet, but had finger trouble uploading, but got there in the end. The new inner box with the door interlocked isolator on also contains the post fire 63 amp BS88-3 fuses added prior to the feed to the distribution board some 10 metres away.
  • Thank you.
    There are a few points.
    It looks a bit cramped in there. The tails into the "isolator" seem to be bent a little too sharply. And why, oh, why has the green and yellow from the DNO's earth rod not been put directly into the "MET", which could have been supplied with more terminals. Best to avoid unnecessary junctions!
    The service head has a sticker, which declares the system to be TN-S. That can only be the case if the G/Y from the earth rod is also connected at the origin of the service cable. And then, I suppose, the DNO is promising that there are no N-PE joints anywhere back to the transformer.
  • Yes, I agree about the tight bends, and also know that the other customer, about 1010 metres before them, had Ze low enough to "call it" TNC-S, and DNO provided their N-PE connection, and may well have added an earth rod there too.
    After my report to the meter owner via the customer, emailed to them yesterday, this was their reply to the customer received today:
    "Thank you for your response. I want to assure you that the issue with the original meter burning was an isolated incident, and we have taken all necessary steps to ensure that it will not happen again. Your current meter is safe, and we are confident that you will not experience this problem in the future.
    If there is anything else we can do to address your concerns or if you would like us to take any further actions, please let us know. Your peace of mind is very important to us.
    I hope that the above has resolved the complaint to your satisfaction. Please contact me within 3 days to confirm that you are happy to close your complaint.
    If we don't have a response from you in 3 days, we will follow up to confirm your complaint is closed.
    Alternatively, if you are an existing customer and have online access, you can close your complaint by logging into your online account and accessing the complaint tracker at ScottishPower - Track My Complaint.
    If, however, you have any further concerns that have not been addressed, please let me know and I will be happy to review these for you."
    I read it as acceptance that their meter (or their connection to/from it) was at fault, with the 3 days being a joke, but I've suggested a reply asking them if they are now prepared to consider the customers costs to replace the damaged kit and get up and running again, so we'll see how we go before considering legal advice.
    So some great replies from everyone thank you all, it's also helped my "OldBoy's" brain better understand what is likely to have happened.
  • DNO provided their N-PE connection
    So everybody has TN-C-S from that transformer!
    There is a N-PE bond under my lawn. The DNO knows it, because they made it. I know it because I saw them make it.
    A few yards along, there is a TN-C-S supply. The DNO knows it, because they made it. I know it because I saw them make it.
    So my neighbourhood is TN-C-S. Full stop!
  • but I've suggested a reply asking them if they are now prepared to consider the customers costs to replace the damaged kit and get up and running again, so we'll see how we go before considering legal advice.
    It may be better in the form of a "letter before action" i,e a warning alerting them that the customer expects those consequential damages (costs) to be met by the liable party (SSE or whoever), and if no satisfactory response to that effect is received within 14 days, then the process will be started to recover this through the small claims courts.
    If there are worries about this approach there are a  great many solicitors who give the 1st half hour of advice free, who could  advise on the wisdom / chances of success of such an approach.
    If there is no question they are responsible, then reasonable compensation is due.
    M.
  • I wouldn't assume it's a simple case to sue the electricity supplier.  See https://www.crownofficechambers.com/2012/09/20/smith-v-ukpn-michael-kent-qc-jack-macaulay-represent-victims-fire-damage-tcc/
    Suppliers have previously argued that they can't be held responsible for unexpected overheating of their kit, and have won in court.
  • interesting case and as a precedent a bit disappointing.
  • Thanks again Mike, and note that we have digressed a bit from the topic, but I've hopefully learnt a lot in the process, and will be encouraging the friend to further follow up with both the Meter owner and the DNO, not that they will be needing much encouragement. Naturally, I'll keep the post updated as the situation progresses.
  • Yes, but I would distinguish the cases in that in Smith the cut-outs were all old, and concerned a duty to inspect. It failed on causation inasmuch as the Claimants had not demonstrated that an inspection programme would have prevented the fires. In the instant case, the installation was new.
    In Smith it was common ground that the cut-outs had not been installed negligently [para. 17].
    I would argue res ipsa loquitur - the facts speak for themselves. A meter was fitted. Shortly afterwards, it caught fire and there is no suggestion that any external influence caused the fire. So either the meter was faulty, or it was installed negligently.
    I would hope that the supplier will accept liability. The damages cannot amount to more than a few hundred pounds, and significantly more has been spent replacing the supply.
    Try to avoid litigation as far as possible.
    BTW: is JP on holiday?