13A Switch fuse spur
Hello, Does anyone know if there are regulations stating that the 13A switch fuse spur can run Continuously at is rated current for long hours? I find this intriguing because, when a spur operates at its maximum rating, it tends to overheat, but i can't find any regulation that explicitly states this isn't allowed. The only regulation i can find in the 7671 concern installation cable size, etc. I know that electricians need to take cable size into account during installation but most of them just follow the standard, without considering the 80% rule from current capacity. the issue i have is that, although it's good practice, i can't find a regulation explicity stating this. So, i'm not sure what to rely on when it comes to the regulations. Does anyone have any insights??
  • My personal view is that fused connection units should not be used for a long hour load of more than about 10 amps, say 2.3 or 2.4 Kw. That is however my personal view of good practice and not a regulatory requirement.
    Equipment with a stated nominal loading of 10 amps could use up to 11 amps actual due to a combination of manufacturing tolerances and supply voltage fluctuations.
    I would have little concern with short term or intermittent loading to a full 13 amps nominal, and perhaps 14.2 amps actual.
    For long hour loads exceeding 10 amps, or short term loads exceeding 13 amps nominal, I would consider it best to avoid 13 amp fused connection units entirely, and instead use a dedicated radial circuit from a 16 amp or 20 amp MCB, and a local 20 amp switch if required.
  • The terminals in 13amp fused spurs and screw sizes generally are the same size as in 20 amp switches and double sockets. I suspect the issue is more the 13 amp fuse getting hot  if run at full load rather than the switch terminals.
    I came across a 3.4 kw storage heater plugged in a couple of years ago. I don't know how long it had been like it but the plug was welded in. They only called me out because it was pretty much on fire.
    Gary
  • Thank you for your messages. I did some further digging and came across Regulation 433.1.204 and Appendix 15 of BS 7671, which state that cables should have a minimum current-carrying capacity of 20A and should not be subjected to continuous loads exceeding this for extended periods.
    I agree, this is for ring final circuits only. The pertinent requirement to which I referred is Regulation 433.1:
  • The type testing to ensure compliance uses a 20 A supply with a 14 A load on the output and a further 6 A on the input
    Clause 17 of 1363-4:2023 specifies the operating temperature, and typically, the test is conducted for 8 hours with a 14A load and a 6A load, totaling 20A. :). i know the standards but thank you for your feed back.
    Again, not that simple ... BS 1363-4 actually states 20 A nominal test current used for the type test are actually14 A ± 0.4 A on the load terminals, and a balance of load on supply terminals of 6 A ± 0.4 A.
    So, the test currents used for type testing may well be 13.6 A on the load terminals, and 6.6 A parallel load on the supply terminals.
    What this all means, is that a heating load rated 3 kW at 230 V might actually have a load current up to 15.1 A (or as little as 10.4 A). Similarly, a heating load rated 3 kW at 240 V might have a load current as much as 13.8 A (or as little as 9.6 A).
    So, you see the type test of BS 1363-4 may not even provide sufficient current flowing through the load terminals (and fuse) for a given immersion heater rated 3 kW at 240 V, never mind one rated 3 kW at 230 V ... or indeed an appliance rated at 13 A at 230 V (which may, according to BS EN 60335-1, actually have a nominal load current at 230 V of 13.65 A).
  • It  is fair to say that the minimum standard for a number of 13A things - i.e. plugs and sockets and adaptors etc , as well as fused spurs really, are set in a way that leads to the 'shallow end' products being not designed with continuous service in mind, especially not in a warmer part of the building. Mostly this works, because loads are in fact short term. But spurs next to water heaters, and sockets behind tumble driers do seem to find the limit and fail quite rapidly and frequently.
    Another way to look at this is the 13A range is really rated at 13A for short duration only.
    In reality the current rating of most things is limited by thermal effects, and of course these are time dependant, and also directly affected by the local temperature and ability to sweat the heat off to the environment.
    Apart from EV marked plugs, which are a relatively  new thing and could probably do with more publicity, personally I'd support a similar higher test standard and visible mark for other accessories specifically  intended for long duration full (slightly over) load use.
  • Another way to look at this is the 13A range is really rated at 13A for short duration only.
    Installing an FSU is slightly different, but I suspect that most customers have no idea what an Amp is. Even if they do, it does not seem unreasonable that they would assume that any two devices with plugs attached (by the manufacturer) may be used for as long as they wish (or can afford).
  • Even if they do, it does not seem unreasonable that they would assume that any two devices with plugs attached (by the manufacturer) may be used for as long as they wish (or can afford).
    Agree with this, if an appliance has a BS 1363-1 plug attached by the manufacturer it ought to be suitable for use with the fuse and socket-outlet (give or take ambient temperature ... another discussion perhaps.
    However, this thread is definitely on connection units and determining whether they are suitable for their rated current.
    And to answer that, I believe yes they are suitable for the rated current (13 A) for a number of hours, BUT that doesn't mean you can simply choose to connect an appliance that is rated at 13 A (+ 5 % as per BS EN 60335, or a calculated current from power at nominal voltage also subject to a potential + 5 % tolerance) and assume everything will be OK - and things get more tricky with heating elements, as demonstrated in an earlier post, even ignoring the fact that 3 kW > 13 * 230 (=2990 W).