Can you use the 1.2K.m/W BICC value for soil resistivity if you haven't had the soil tested or should you stick with BS7671 value of 2.5K.m/W? As this has a big impact on cable sizes?
Depends where on the planet you are. Remember that BS7671 is not just for the UK , but also for many of the 230V parts of the middle east, Malta and probably a few other hot dry places too. The UK soil, especially where it is wet clay, is a lot better conductor of heat than the dry dust worst case, and the BICC figures reflect this. Actually so does BS7671, more or less, if you put in the same values and use the rating factors - just the default is more cautious.
UK DNOs and similar know the soils on their patch, and may appear to sail closer to the wind than BS7671 allows, but have few problems in reality.
Some typical figures for the inverse of what you need - conductivity in W/(m.K)
note the huge effect on sand when it goes from dry (~ 0,5 W/(m.K) == 2.0 K.m/W )
to saturated (~ 2 W/(m.K) == 0.5 K.m/W )
Clay has less of a range, unless its frozen when suddenly its cooling properties are superb.
Really the cooling of a test cable should be measured if there is a lot at stake, but usually its not worth the aggro, and one has to be confident as to how things will vary with season.
My opinion is that it depends on installation.
It's simply not feasible to distribute large amounts of power via underground cables when the cable calcs are performed on the basis that the ground thermal resistivity is 2.5 K.m/W. Cable sizes become borderline impossible to terminate and the cost per metre of the trench and cable sky rocket. Have a read of ENA TS 97-1 or search up Cement Bound Sand (CBS)... CBS has a thermal resistivity of <1.2 K.m/W.
The same table or ones very like it appear in a number of places, but https://www.cableizer.com/documentation/k_4/ is the one I lifted the graphic from, as the formatting is nice. I'm not too sure who is copying who, and how old the original research actually is.
More to the point if you are looking at more than a few £k of cables, it does become worth putting in the effort to do a test cable heating measurement in the local ground, or if needed to back fill the channels with material that is selected to improve the cooling rather than just lobbing back what was dug out. That however needs good control of who is doing it, and not perhaps the cheapest un-inspected contract labour - who may skimp on the expensive 'fancy sand' due to not realising why it is important.
Or stay at HV until nearer the load (!) nothing like having fewer amps to keep things small and neat. For high enough power levels, such things become economic, although the regulatory hurdles as to who can do that work, set that bar quite high in the UK.