1.2K.m/W BICC value for soil resistivity or BS7671 value of 2.5K.m/W?

Can you use the 1.2K.m/W BICC value for soil resistivity if you haven't had the soil tested or should you stick with BS7671 value of 2.5K.m/W? As this has a big impact on cable sizes?

Parents
  • The guidance in BS 7671 is for cables in and around buildings.

    Other approaches are not precluded but the designer is responsible for selecting an appropriate approach for the particular conditions pertaining to the installation.

Reply
  • The guidance in BS 7671 is for cables in and around buildings.

    Other approaches are not precluded but the designer is responsible for selecting an appropriate approach for the particular conditions pertaining to the installation.