Hello
We are seeking a self employed Chartered Engineer to carry out a site visit where the electrical system can be inspected/viewed. The customer has asked for 2 separate earthing systems.
So, we require someone who can visit site (Tamworth area), inspect the arrangement and advise/produce a report of findings and possible alternative options?
Is there someone here who can assist with this?
Kind regards
Zoe Wheeler
  • Hi Zoe,
    Why are two separate systems required? Are any of the supplies at HV (or sharing the earthing system with an HV supply)?
  • Or radio (e.g. HAM rig) or just TT for an outbuilding or EVs?
  • I am a radio ham and a CEng if that helps PM me?
  • Morning
    The earthing system coming into factory at present is TNS system. However the process installation team have put 4 control rooms in using 3 ph N&E but other control rooms that they have installed are only using 3ph & E - no Neutral.
    We have given our opinion to the client and also the process installation team have had their opinion heard by the factory. However the client/project manager wants an independent view/opinion on this and a report of the findings/opinion/best way forward.
    To conclude, not using a neutral in the other panels will cause any conflict in the earthing system.
  • I am not sure that the forum has a PM facility anymore? You can contact me on info ( the symbol for at)astutetechnicalserivices.co.uk
  • Hi John, thank you for your message - I have sent you an email now.
  • There is generally no issue with 3P and E without N, actually it is quite common for single items of machinery , but only if none of the loads connected require a neutral connection - i.e. have a single phase aspect.
    What should ring alarm bells is if someone is hoping to use the earth as a substitute for the missing neutral for some load that is not perfectly 3 phase balanced. This would cause current to flow in the earthing even in a non-fault condition. In the UK this is a big no-no, although seen in imported kit sometimes, and often the easiest fix for a small single phase load is to add a transformer wired between 2 phases on the primary to step down to the single phase supply voltage needed to supply the out of balance load(s).
    Obviously if more than a little current is needed then it is better to supply a 'real' neutral.
  • Thank you so much for your response - it is much appreciated, and is along the same thinking as us. The site in question just needs this information in a report form following a site visit.