Chartered engineer required for a small job

Hello

We are seeking a self employed Chartered Engineer to carry out a site visit where the electrical system can be inspected/viewed. The customer has asked for 2 separate earthing systems.

So, we require someone who can visit site (Tamworth area), inspect the arrangement and advise/produce a report of findings and possible alternative options?

Is there someone here who can assist with this?

Kind regards

Zoe Wheeler

Parents
  • Hi Zoe,

    Why are two separate systems required? Are any of the supplies at HV (or sharing the earthing system with an HV supply)?

  • Or radio (e.g. HAM rig) or just TT for an outbuilding or EVs?

  • Morning

    The earthing system coming into factory at present is TNS system. However the process installation team have put 4 control rooms in using 3 ph N&E but other control rooms that they have installed are only using 3ph & E - no Neutral.

    We have given our opinion to the client and also the process installation team have had their opinion heard by the factory. However the client/project manager wants an independent view/opinion on this and a report of the findings/opinion/best way forward.

    To conclude, not using a neutral in the other panels will cause any conflict in the earthing system.

  • There is generally no issue with 3P and E without N, actually it is quite common for single items of machinery , but only if none of the loads connected require a neutral connection - i.e. have a single phase aspect.

    What should ring alarm bells is if someone is hoping to use the earth as a substitute for the missing neutral for some load that is not perfectly 3 phase balanced. This would cause current to flow in the earthing even in a non-fault condition. In the UK this is a big no-no, although seen in imported kit sometimes, and often the easiest fix for a small single phase load is to add a transformer wired between 2 phases on the primary to step down to the single phase supply voltage needed to supply the out of balance load(s).
    Obviously if more than a little current is needed then it is better to supply a 'real' neutral.
    Mike.

Reply
  • There is generally no issue with 3P and E without N, actually it is quite common for single items of machinery , but only if none of the loads connected require a neutral connection - i.e. have a single phase aspect.

    What should ring alarm bells is if someone is hoping to use the earth as a substitute for the missing neutral for some load that is not perfectly 3 phase balanced. This would cause current to flow in the earthing even in a non-fault condition. In the UK this is a big no-no, although seen in imported kit sometimes, and often the easiest fix for a small single phase load is to add a transformer wired between 2 phases on the primary to step down to the single phase supply voltage needed to supply the out of balance load(s).
    Obviously if more than a little current is needed then it is better to supply a 'real' neutral.
    Mike.

Children
  • Thank you so much for your response - it is much appreciated, and is along the same thinking as us. The site in question just needs this information in a report form following a site visit.