Connection of back-upgenerator to TN-C-S domestic installation

Hi All. I'm a medically retired electrician with additional strings to the bow throughout my career. From contracting on commercial electrical installations to building/designing large industrial containerised generators to managing landfill gas generator installations and finishing at building maintenance engineer covering alot of variable skills with HVAC and BMS.

I try to keep the mind busy and do what I can. 

Appreciate your viewing my question I'll try to be as descriptive as possible. 

My home is TN-C-S supply with no extraneous parts ( water supply is plastic pipe and no gas supply).

Approximately 5 years ago I installed a large metal garage/workshop 7.5m by 4.5m(concrete floor with metal box section frame bolted to the concrete pad) 

I supplied the garage with a 6mm armoured  via 30ma RCD and 40amp MCB ,armour being connected to house distribution board and isolated at the garage termination so as not to export the earth as per regulation,I installed 2m deep electrode and additional 1m deep electrode both wired back to garage DB. So in effect garage is on a TT system.

The house distribution boards (8 way mem bs88 and 4 way mem2000 RCD mcb) I want to change out for 1 large regulation DB , one in looking at is MK dual 100amp 30ma isolator with type 2 SPD rest populated with mcb's.

To the nub of my question. I want to install back up generator (7.5kva peak 6.25kva constant)which will be sited out the back of the metal garage( outside garage building not inside)some approx 12m from house. I'll give you my thoughts on what I'm thinking of installation to ensure complete separation from incoming mains supply to remove chance of any back feed especially under fault condition.

1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.

2.Wired back to a 20amp double pole rcbo enclosure in distribution cupboard.

3.From rcbo into a manual 3 pole  transfer switch.

4.The network supply wired the manual 3 pole transfer switch then from transfer switch to new distribution board (dB).

5. The generator chassis will be connected to garage earth electrodes when in use.

6.. 3 pole manual transfer switch? My thinking is to switch L. N. and the earth. 

My thinking on this: when mains is in use garage supply has isolated earth DB side connected only  as previously discussed to protect cable/circuit going to garage rest of house still using supplier earth path . 

When generator supply is used the whole installation house including garage would be effectively TT system this way no chance of back feed to the supplier network including under fault conditions from my/consumer end giving earthing is also switched at the manual transfer switch, i

Q.1.is this 3 pole manual transfer idea (switching earths) idiotic/unnecessary/ not advisable ?

Q. 2. Should I include a type 1 SPD to the 20amp 30ma generator supply enclosure inside distribution cupboard given large metal shed and lighting strikes ? 

Sorry for long winded pre log just trying to ensure you've all the information needed. Would be grateful for your thoughts and indeed advice.

Parents
  • 1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.

    You're probably thinking correctly, but just to be absolutely clear (in formal terms and for others reading this) the thing on the outside of the house should be a plug (inlet), rather than a socket - the trailing part (from the generator) should have shrouded socket tubes, rather than exposed pins.

    When generator supply is used the whole installation house including garage would be effectively TT system

    The generator's system would almost certainly be TN-S - the local electrode acting as the "source" earthing (the first T) and c.p.c.s connected to N via the generator's N-PE link (so TN). To create a local TT system, you'd need two separate electrodes, for for the generator and another for the installation.

    The usual approach is you use a DP change-over switch (for single phase) and have Earth solidly connected to both a local electrode and the DNO's earth. In Grid mode it's then TN-C-S as before, and TN-S in generator mode.

    You local TT sub-installation for the workshop makes things more interesting. You could leave that as TT, even in generator mode, but you'd need at least two electrodes then, one for the generator and another separate one for the garage/workshop. You just need to make sure that the sum of the two electrode resistances is still gives a low enough loop impedance for ADS etc for your TT system (as your generator electrode is likely to have a higher resistance to Earth than the DNO's).

    One problem with that approach though is the proximity of the generator to the workshop - if it's within reach (2.5m?) they need to be on the same earthing system - which they won't be if the workshop is TT and the house TN. One option then is to bring the workshop onto the house TN system during island mode - perhaps a 3rd pole in your change-over switch could achieve that - but you'd have to be very careful how things were arranged both in grid-connected and island mode - as you'd want to ensure the workshop wasn't connected to the DNO earth, or within reach of the DNO earth, at any time, including when in island mode. Rating a change-over switch contacts to switch between a DNO Earthing facility and extraneous-conductive-parts (e.g. the workshop, presuming it's sat on the ground) can get "interesting" as the currents involved may include distribution network diverted neutral currents, which aren't related to the generator's output rating (consider why you might need 10mm2 main bonding even for tiny installations).

    Maybe one option to consider is to make both the house and workshop one common earthing system - TT in grid mode and TN-S in island mode.

    Diagrams often help. For starters, here's one I prepared for earlier threads, for a simple change-over arrangement:

       - Andy.

  • p.s don't know how these forum things work will everyone that's contributed see this or do i need to send to them individually

    It's a public forum - everyone sees everything! If you mention someone in particular they likely get a notification as well.

      - Andy.

  • lol i get that just didn't know cos they where on thread they'd get notification individually. Thanks 

  • Hi Andy, handy illustration thank you.

    Maybe just one small point, what i was suggesting is that during mains fail and generator is to be used, the generator earthing connection  is linked to the existing garage earth pit electrode and removed after generator use.

    1. Install generator behind metal garage outside of the building, with neutral earth link in windings and chassis/engine/alt connected to earth pit electrode (one of the two pits of electrodes linked together currently to garage db for metal garage TT set up from house TN-C-S supply, supply cable earthed at house db isolated at garage).

    with this in mind all should be equipotential, and all earths inside and out have physical cabling connection during generator use. 

  • Maybe just one small point, what i was suggesting is that during mains fail and generator is to be used, the generator earthing connection  is linked to the existing garage earth pit electrode and removed after generator use.

    OK, so with the generator plugged in, would the workshop's earthing system be connected to the PME Earth? (defeating the TT'ing of it)

      - Andy.

  • Yes ,that was my thoughts buddy so in generation mode all earth's are linked externally and internally by earth link from existing earth pit electrode to genset frame, chassis etc then via earth in generator supply cable to house inlet ,house inlet internally connected to MET. When on mains supply again , generator supply cable removed garage is back on TT.

  • While running on genset, the system is TN-S, with a connection to a DNO earth that is only acting as either as an additional electrode or perhaps an extraneous part in that mode.

    To the DNO it is PME/TNCs but the neutral the DNO earth is combined with is not the  one that is in use for neutral current when on genset.

    It also may or may not be disconnected in whole or in part, if the DNO side of things is off and being worked on, so it can't be considered as the main means of earthing.

    Mike.

  • Hi Mike I do agree in your summation in principle, there are some things to note.

    While running on genset, the system is TN-S, with a connection to a DNO earth that is only acting as either as an additional electrode or perhaps an extraneous part in that mode.

    The earth connection from the generator "when generator is running"(no mains supply) is only connected to the DNO via the earth withing the power supply coming into house from said generator.  If you see in the detail above the generator/chassis /engine itself when running is connected via10mm earth cable connected to 1 earth pit electrode (of which there are 2 pits, them selves linked together for the Garage supply.

    What you highlight ref DNO connection is why originally i wanted to switch the earth within the "break before make bypass" so in generator mode all earthing inside and out would be only referenced back to earthing electrodes.

    It also may or may not be disconnected in whole or in part, if the DNO side of things is off and being worked on, so it can't be considered as the main means of earthing.

    I totally agree, again why i wanted to switch the earth so in generator mode my home is completely as an "island" with no ref to DNO because if there is a mains failure 99% fault is on their line/network.

    From my reading and understanding switching the earth would be within regulations but opened my question to forum for advise and thoughts, alot of very helpful and knowledgeable people on here .

  • OK, so more like this then?

    I presume you've TT'd the workshop to avoid exporting PME earth to the steel structure outdoors (PME earths not always being close to true Earth potential, especially during network problems, a broken PEN being the extreme example). But with this setup at the at the very time the PME earth is most likely to be hazardous (when the distribution network is playing up), you're deliberately connecting it to the workshop? That doesn't feel ideal somehow.

    Also in that setup the workshop would be an extraneous-conductive-part w.r.t. the PME earth - so the connection would have to meet the requirements of a main bond - i.e. min 10mm² all the way (which means quite a chunky flex for the generator and suitable sized plug & inlet).

    If you wanted to have the workshop TT and at have the house/generator in the same equipotential zone as the workshop, one solution might be to TT the house as well (and don't have any connection to the PME Earth). Often that's not practical as bonds to metallic services can defeat the isolation, but in your case with plastic water/gas that might work.

    Alternatively keep PME for the house, but arrange things so the genny and workshop are out of reach of each other - e.g. locate the generator further away or interpose and insulating barrier (wooden fence) or similar.

      - Andy.

  • earth pit electrode (one of the two pits of electrodes

    For those times when those two electrodes are not locally/directly connected, what is the impedance between them?

    If I understood correctly you are, at times, using them independently to separate between two earthing 'systems' [hence their 'boundaries' become important], and others, such as the DNO may have assumed different boundaries in their design process Grimacing.

  • Hi Phillip, Thankyou for your contribution.

    The (both earth pit electrodes which are 4m apart fyi) are not at any instanced used separately/independently nor do they rely on impedance reading between them for conductivity. Both earth rod pit electrodes are permanently connected together by means of 2off 10mm earthing cables from each pit (4off 10mm cables)  which are terminated in an esco under the db board inside the garage and form the TT system earthing only. From this esco earth cable goes to garage db and again from esco to framework of the garage.

    The proposed earthing connection to the generator alt/engine/chassis (which will be sited within touching distance of the metal garage) was a 10mm earthing cable to nearest earth pit electrode (some 3-4 metres from the genset)  for clarity no earthing cabling is to be disconnected from the existing, just the addition of another cable from the earth pit electrode to the genset, for a result of equipotential bonding of extraneous conductive parts and to provide path for earth fault current .

    There is no ability for direct contact between the metal garage and house (including any exposed conductive parts of house) due to distance between them..

    The DNO incomer to the house is 8m from 1st earth pit electrode for the garage.

    When i get a chance ill get readings between the two (DNO TN-C-S and TT earth )will also clamp for any earth fault current at DNO.

    From memory earth electrodes to garage db are .2 ohms and several points around the frame of garage do not exceed .6ohms after allowance for fly lead .

Reply
  • Hi Phillip, Thankyou for your contribution.

    The (both earth pit electrodes which are 4m apart fyi) are not at any instanced used separately/independently nor do they rely on impedance reading between them for conductivity. Both earth rod pit electrodes are permanently connected together by means of 2off 10mm earthing cables from each pit (4off 10mm cables)  which are terminated in an esco under the db board inside the garage and form the TT system earthing only. From this esco earth cable goes to garage db and again from esco to framework of the garage.

    The proposed earthing connection to the generator alt/engine/chassis (which will be sited within touching distance of the metal garage) was a 10mm earthing cable to nearest earth pit electrode (some 3-4 metres from the genset)  for clarity no earthing cabling is to be disconnected from the existing, just the addition of another cable from the earth pit electrode to the genset, for a result of equipotential bonding of extraneous conductive parts and to provide path for earth fault current .

    There is no ability for direct contact between the metal garage and house (including any exposed conductive parts of house) due to distance between them..

    The DNO incomer to the house is 8m from 1st earth pit electrode for the garage.

    When i get a chance ill get readings between the two (DNO TN-C-S and TT earth )will also clamp for any earth fault current at DNO.

    From memory earth electrodes to garage db are .2 ohms and several points around the frame of garage do not exceed .6ohms after allowance for fly lead .