Connection of back-upgenerator to TN-C-S domestic installation

Hi All. I'm a medically retired electrician with additional strings to the bow throughout my career. From contracting on commercial electrical installations to building/designing large industrial containerised generators to managing landfill gas generator installations and finishing at building maintenance engineer covering alot of variable skills with HVAC and BMS.

I try to keep the mind busy and do what I can. 

Appreciate your viewing my question I'll try to be as descriptive as possible. 

My home is TN-C-S supply with no extraneous parts ( water supply is plastic pipe and no gas supply).

Approximately 5 years ago I installed a large metal garage/workshop 7.5m by 4.5m(concrete floor with metal box section frame bolted to the concrete pad) 

I supplied the garage with a 6mm armoured  via 30ma RCD and 40amp MCB ,armour being connected to house distribution board and isolated at the garage termination so as not to export the earth as per regulation,I installed 2m deep electrode and additional 1m deep electrode both wired back to garage DB. So in effect garage is on a TT system.

The house distribution boards (8 way mem bs88 and 4 way mem2000 RCD mcb) I want to change out for 1 large regulation DB , one in looking at is MK dual 100amp 30ma isolator with type 2 SPD rest populated with mcb's.

To the nub of my question. I want to install back up generator (7.5kva peak 6.25kva constant)which will be sited out the back of the metal garage( outside garage building not inside)some approx 12m from house. I'll give you my thoughts on what I'm thinking of installation to ensure complete separation from incoming mains supply to remove chance of any back feed especially under fault condition.

1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.

2.Wired back to a 20amp double pole rcbo enclosure in distribution cupboard.

3.From rcbo into a manual 3 pole  transfer switch.

4.The network supply wired the manual 3 pole transfer switch then from transfer switch to new distribution board (dB).

5. The generator chassis will be connected to garage earth electrodes when in use.

6.. 3 pole manual transfer switch? My thinking is to switch L. N. and the earth. 

My thinking on this: when mains is in use garage supply has isolated earth DB side connected only  as previously discussed to protect cable/circuit going to garage rest of house still using supplier earth path . 

When generator supply is used the whole installation house including garage would be effectively TT system this way no chance of back feed to the supplier network including under fault conditions from my/consumer end giving earthing is also switched at the manual transfer switch, i

Q.1.is this 3 pole manual transfer idea (switching earths) idiotic/unnecessary/ not advisable ?

Q. 2. Should I include a type 1 SPD to the 20amp 30ma generator supply enclosure inside distribution cupboard given large metal shed and lighting strikes ? 

Sorry for long winded pre log just trying to ensure you've all the information needed. Would be grateful for your thoughts and indeed advice.

  • So DNO TN-C-S supply now offline, completely isolated, and with it the regulations covering the same TN-C-S supply within customers installation, different supply different regulations now apply

    Not always, you may be connected through extraneous-conductive-parts (gas, water, structural parts of the building, either via direct connection, or due to their proximity to the PME supply cable underground).

    different supply different regulations now apply

    No, ESQCR applies still, you would be operating 'switched alternative' supply to the DNO supply according to Regulation 21 of ESQCR (or Regulation 22 of the ESQCR NI), for which G99 applies, as well as BS 7671. 

    The reason the DNOs support this approach, is there may well be other installations "live" in your area, even if yours is islanded and you have no grid power.

    If I thought there was a way you could argue round this, or some magic of taking away the fact that if your main building has extraneous-conductive-parts, you'd still be connected to PME, I would say so. 

    As I said above, these permutations have been debated.

  • earth pit electrode (one of the two pits of electrodes

    For those times when those two electrodes are not locally/directly connected, what is the impedance between them?

    If I understood correctly you are, at times, using them independently to separate between two earthing 'systems' [hence their 'boundaries' become important], and others, such as the DNO may have assumed different boundaries in their design process Grimacing.

  • If we're to avoid connecting the workshop to PME, I think we've got (at least) 3 options...

    1. Keep the house connected to PME, the workshop TT, and somehow put the generator out of reach of the workshop.

    2. As above, but with some kind of switching to disconnect the DNO's earth when running off the generator (can only work if there are no extraneous-conductive-parts than can import a PME potential from neighbouring properties, and suitable separation from any buried metalwork (and cables) connected to PME).

    3. Just TT the lot (Everything TN-S in off-grid mode, house and workshop on same earthing system all the time) (similar provisos for separation from PME).


    (I've added an up-front RCD on the grid supply for the last one, but it could go after the change-over, or even be omitted if there was double/reinforced insulated all the way to the 1st RCD).

    I suppose you could have a variant of 2 where the PE change-over switch connects the workshop PE to the house MET....

      - Andy.

  • Rewinding to the beginning, would it be easier to run a sufficiently large earth wire to the workshop and make it PME, along with the house?

    A lot of DNOs don't like PME being used for metal outbuildings (but the rules do seem to vary by region) - same reasoning as EVs or caravans - there's a (small) risk of shock for someone outside stood on the ground and touching the building (or door handle, if the door is also steel).

       - Andy.

  • Hi Phillip, Thankyou for your contribution.

    The (both earth pit electrodes which are 4m apart fyi) are not at any instanced used separately/independently nor do they rely on impedance reading between them for conductivity. Both earth rod pit electrodes are permanently connected together by means of 2off 10mm earthing cables from each pit (4off 10mm cables)  which are terminated in an esco under the db board inside the garage and form the TT system earthing only. From this esco earth cable goes to garage db and again from esco to framework of the garage.

    The proposed earthing connection to the generator alt/engine/chassis (which will be sited within touching distance of the metal garage) was a 10mm earthing cable to nearest earth pit electrode (some 3-4 metres from the genset)  for clarity no earthing cabling is to be disconnected from the existing, just the addition of another cable from the earth pit electrode to the genset, for a result of equipotential bonding of extraneous conductive parts and to provide path for earth fault current .

    There is no ability for direct contact between the metal garage and house (including any exposed conductive parts of house) due to distance between them..

    The DNO incomer to the house is 8m from 1st earth pit electrode for the garage.

    When i get a chance ill get readings between the two (DNO TN-C-S and TT earth )will also clamp for any earth fault current at DNO.

    From memory earth electrodes to garage db are .2 ohms and several points around the frame of garage do not exceed .6ohms after allowance for fly lead .

  • Rewinding to the beginning, would it be easier to run a sufficiently large earth wire to the workshop and make it PME, along with the house?

    It might ... BUT some DNOs (and depending how large the metal building is, industry guidance) might not "like" connecting the workshop to PME,

    Whilst the "not PME" guidance for large metal buildings is certainly founded in fact, the carte-blanche application of "TT the outbuilding" is definitely not good, and very limiting given Regulation 411.3.1.1.

    This, and the overall "simultaneous contact" issue, has caused no end of trouble since EV charging came on the scene, even though the approach (formerly the EEB of EEBADS as we used to call it) has been here for some considerable time. As ever, the unforeseen nuances will ever trip us up.

  • 2. As above, but with some kind of switching to disconnect the DNO's earth when running off the generator (can only work if there are no extraneous-conductive-parts than can import a PME potential from neighbouring properties, and suitable separation from any buried metalwork (and cables) connected to PME).

    1. and 3. of your post, I'd support. However, 3. could be costly, perhaps fraught with issues, and may not result in separation from PME (or the relevant issues) ... whilst ticking the boxes in reality, in some installations, could just cost money for no benefit.

    BUT ... 2. I'm really not sure about at all, given G99, and other existing guidance (IET CoP for Electrical Energy Storage Systems, for example) ... and again, might not actually achieve anything if you're still fortuitously connected to PME.

    Not easy.

  • Correct .

  • Hi Andy, this is turning into a head melter for me at least thinking solution is one way and not realising other areas to consider , like I've said I'm grateful for all the input and ideas as to solution, like yourself gkenyon very knowledgeable chaps and patient , while my brain tries to catch up.

    Item 1 is possible as i have a wooden shed behind the back of the metal garage if genset was in there even with door open is approx 3 metres from metal garage .

  • Item 1 is possible as i have a wooden shed behind the back of the metal garage if genset was in there even with door open is approx 3 metres from metal garage .

    BUT ... still no way of using the workshop earth electrode in 'island mode' ...