Connection of back-upgenerator to TN-C-S domestic installation
Hi All. I'm a medically retired electrician with additional strings to the bow throughout my career. From contracting on commercial electrical installations to building/designing large industrial containerised generators to managing landfill gas generator installations and finishing at building maintenance engineer covering alot of variable skills with HVAC and BMS.
I try to keep the mind busy and do what I can.
Appreciate your viewing my question I'll try to be as descriptive as possible.
My home is TN-C-S supply with no extraneous parts ( water supply is plastic pipe and no gas supply).
Approximately 5 years ago I installed a large metal garage/workshop 7.5m by 4.5m(concrete floor with metal box section frame bolted to the concrete pad)
I supplied the garage with a 6mm armoured  via 30ma RCD and 40amp MCB ,armour being connected to house distribution board and isolated at the garage termination so as not to export the earth as per regulation,I installed 2m deep electrode and additional 1m deep electrode both wired back to garage DB. So in effect garage is on a TT system.
The house distribution boards (8 way mem bs88 and 4 way mem2000 RCD mcb) I want to change out for 1 large regulation DB , one in looking at is MK dual 100amp 30ma isolator with type 2 SPD rest populated with mcb's.
To the nub of my question. I want to install back up generator (7.5kva peak 6.25kva constant)which will be sited out the back of the metal garage( outside garage building not inside)some approx 12m from house. I'll give you my thoughts on what I'm thinking of installation to ensure complete separation from incoming mains supply to remove chance of any back feed especially under fault condition.
1. Install a single phase 32amp incomer socket ( will be supplied from generator in event of outage)to the exterior of house.
2.Wired back to a 20amp double pole rcbo enclosure in distribution cupboard.
3.From rcbo into a manual 3 pole  transfer switch.
4.The network supply wired the manual 3 pole transfer switch then from transfer switch to new distribution board (dB).
5. The generator chassis will be connected to garage earth electrodes when in use.
6.. 3 pole manual transfer switch? My thinking is to switch L. N. and the earth.
My thinking on this: when mains is in use garage supply has isolated earth DB side connected only  as previously discussed to protect cable/circuit going to garage rest of house still using supplier earth path .
When generator supply is used the whole installation house including garage would be effectively TT system this way no chance of back feed to the supplier network including under fault conditions from my/consumer end giving earthing is also switched at the manual transfer switch, i
Q.1.is this 3 pole manual transfer idea (switching earths) idiotic/unnecessary/ not advisable ?
Q. 2. Should I include a type 1 SPD to the 20amp 30ma generator supply enclosure inside distribution cupboard given large metal shed and lighting strikes ?
Sorry for long winded pre log just trying to ensure you've all the information needed. Would be grateful for your thoughts and indeed advice.
  • Hi gkenyou, many thanks again for you input, mmm , im going to test today from nearest disconnected  earth electrode(garage TT) to DNO MET,  with from what i can ascertain ive no exposed conductive parts in the house installation (gas pipe or water) the DNO cable appears to have insulated outer, just out of interest.
  • Garage is 4.2m x 7.1m, , 2.43m to the eaves and 3.35 at peak
  • Well that was interesting , on checking at DNO supply in house, no fault current or voltage on earth fine. Disconnected the earthing cables from the earth pit electrode ( at garage) nearest the house (approx 8 m from DNO TN-C-S incomer) from disconnected earth electrode to DNO earth .1ohm and the .1ohm was the fly lead resistance
  • 0.1Ω ain't soil resistance around an electrode resistance - that's more like a continuous metallic path. There's something odd going on - maybe some connection remains or the electrode has been driven into a buried cable or pipe....
  • Hi Andy, That's what i was thinking , couldn't believe the read, was speaking with the neighbour (semi detached)and when he got his houses renovated couple years back whoever did the electrics drove 8ft of earth electrode in into the ground in the outside wall from the db and tied it  to TN-C-S MET so my supply likely id getting grounded direct from next door , i had done my garage before he'd renovated , im glad you all with your replies made me question myself as i was fairly sure i had good separation, just shows never assume lol rule 101 electrically even in our own properties.
  • Out of curiosity, what sort of instrument did you use to get the 0.1Ω reading? I find that conventional d.c. Ohmmeters can be easily fooled by stray voltages - a loop tester does better (e.g. using the mains L as reference) - technically you're not measuring quite the same thing, but the DNO's side is usually pretty low impedance and any over-estimate errs on the side of safety when used as your own electrode resistance. I'm having difficulty in believing that there's any amount of soil in a 0.1Ω reading...