Could you please confirm whether clause 431.1.1 (iii) in BS 7671 is accurate and up to date?

As per the requirements of BS 7671, a circuit breaker may take up to one hour to trip when subjected to a current of approximately 1.45 times its rated current. In such cases, we would like to clarify whether the associated cable is also designed to withstand 1.45 times its continuous current-carrying capacity for the same duration without degradation or thermal damage.

Is this aspect covered in any cable standards (such as BS 6004, IEC 60287, or IEC 60364) or specified in cable manufacturer datasheets?

We seek clarification on whether:

  • The cable’s short-term thermal endurance aligns with the breaker’s tripping characteristics.

  • Manufacturers consider this 1.45 × In scenario when defining safe operational limits.

Any references or guidelines from standards or datasheets that confirm the cable's ability to tolerate such overloads for a limited duration would be helpful.

Parents
  • Sorry, please read it as 433.1.1

  • Thank you, in that case, the following answer I gave is relevant:

    In terms of the question: we would like to clarify whether the associated cable is also designed to withstand 1.45 times its continuous current-carrying capacity for the same duration without degradation or thermal damage.

    The key to understanding this requirement is that Iz is the current-carrying capacity of a cable for continuous service under the particular installation conditions concerned. For determination of Iz, see Appendix 4 to BS 7671. Where the cable types (or conditions) are not covered in Appendix 4, other approaches are not precluded, including BS EN 20287 series and BS 7769 series.

  • Thank you for your response. I would like to seek clarification regarding the application of the 1.45 factor to Iz (the continuous current-carrying capacity of cables). On what basis was this factor of 1.45 established? Can cables reliably withstand 1.45 times their rated continuous current, and is this value supported or referenced in any specific cable standards?

  • Can cables reliably withstand 1.45 times their rated continuous current

    Yes ... but not for an indefinite time. Hence, also the requirement of Regulation 433.1 'Every circuit shall be designed so that small overload of long duration is unlikely to occur'.

    The design element that is intended to ensure that the cable is not overloaded is covered in the first two conditions of 433.1.1, i.e. 433.1.1(i) and 433.1.1 (ii), which states, in effect:

    Ib≤In≤Iz

    The missing piece of the puzzle lies between In and a full blown fault current (Section 434). For protection against fault current in general, Regulation 434.5 applies ... Regulation 434.5.2 makes the assumption (because the short duration of the high current fault), that no heat is lost from the outside of the cable during the fault ... we call that an 'adiabatic approach'.

    For faults currents that take over 5 seconds or so to disconnect, the estimates of the adiabatic approach no longer apply, and more current can be handled than the formula in 434.5.2 shows. We can then use the 'non-adiabatic approach' explained in BS 7454 to calculate what the cable can withstand.

  • It is there because you have to have a gap between the current that any real breaker can carry all day without tripping - it's full load current, and a higher value, the highest current it might not trip at. Above that are current levels at which it certainly will operate, with increasing speed with increasing currents.

    That 1.45 figure is the width of that uncertain region.

    So a 32A breaker can take 32A all day , at full temperature. It is certain to trip within 1 hour at around 40A, but between 32A and 40A is a grey area, where what it does will depend on the day, and where in the natural scatter of the production line that one particular breaker sits.

    The cable rating is a function of cable size, its location, grouping with other cables etc, and is a matter for the designer to allow for this - normally you'd not put a 40A load on a 32A breaker  for example. 
    Mike.

    PS cables can take massively more than their continuous rating for short periods, it is the race between the cable heating from the overload and cooling to the environs - and at what temperature a final equilibrium is reached.

  • We can then use the 'non-adiabatic approach' explained in BS 7454 to calculate what the cable can withstand.

    You can read more about this approach in Section 6.5 of the IET Commentary on the IET Wiring Regulations.

    Section 6.7 of the same publication goes on to discuss the application of the techniques for flexible cables.

    Regulation 433.1.1 is also explained on Page 28 of the IET's Guidance Note 6: Protection against overcurrent, which states:

    Condition (iii) provides the overload protection required by Regulation 433.1.1, but note that it is concerned primarily with the conductors. Protection for electrical equipment in the circuit, including the overload device itself, should be covered by careful selection of equipment, made to a standard quoted in BS 7671 or to an equivalent.

    The factor 1.45 in condition (iii) is based on a combination of experience and investigation. This has shown that the types of cable considered in BS 7671 can safely withstand a small but undefined number of periods at excess temperatures corresponding to currents not greater than 1.45 times their current-carrying capacity. However, such currents must not persist for long periods.

Reply
  • We can then use the 'non-adiabatic approach' explained in BS 7454 to calculate what the cable can withstand.

    You can read more about this approach in Section 6.5 of the IET Commentary on the IET Wiring Regulations.

    Section 6.7 of the same publication goes on to discuss the application of the techniques for flexible cables.

    Regulation 433.1.1 is also explained on Page 28 of the IET's Guidance Note 6: Protection against overcurrent, which states:

    Condition (iii) provides the overload protection required by Regulation 433.1.1, but note that it is concerned primarily with the conductors. Protection for electrical equipment in the circuit, including the overload device itself, should be covered by careful selection of equipment, made to a standard quoted in BS 7671 or to an equivalent.

    The factor 1.45 in condition (iii) is based on a combination of experience and investigation. This has shown that the types of cable considered in BS 7671 can safely withstand a small but undefined number of periods at excess temperatures corresponding to currents not greater than 1.45 times their current-carrying capacity. However, such currents must not persist for long periods.