Could you please confirm whether clause 431.1.1 (iii) in BS 7671 is accurate and up to date?

As per the requirements of BS 7671, a circuit breaker may take up to one hour to trip when subjected to a current of approximately 1.45 times its rated current. In such cases, we would like to clarify whether the associated cable is also designed to withstand 1.45 times its continuous current-carrying capacity for the same duration without degradation or thermal damage.

Is this aspect covered in any cable standards (such as BS 6004, IEC 60287, or IEC 60364) or specified in cable manufacturer datasheets?

We seek clarification on whether:

  • The cable’s short-term thermal endurance aligns with the breaker’s tripping characteristics.

  • Manufacturers consider this 1.45 × In scenario when defining safe operational limits.

Any references or guidelines from standards or datasheets that confirm the cable's ability to tolerate such overloads for a limited duration would be helpful.

Parents
  • Sorry to jump on the back of this but can I just ask about the effect of indent (iii) on the 3036 fuse? I understand the derivation of the correction factor of 0.725 as it comes from the declared fusing factor of a 3036 fuse of 2*In at a time of 4 hours thus when applied to the formula in indent (iii), Iz>In/0.725.  

    However, referring to Appendix 3 for 5A,15A and 30A 3036 fuses, the value I2 seems to be as good as a similarly rated BS88-2 or 88-3 fuse . I2 for other In values of 20A, 45A and 100A 3036 fuses do seem to have a much extended I2 time. 

    So is the 0.725 correction factor applicable to some, but not all, 3036 fuses?

Reply
  • Sorry to jump on the back of this but can I just ask about the effect of indent (iii) on the 3036 fuse? I understand the derivation of the correction factor of 0.725 as it comes from the declared fusing factor of a 3036 fuse of 2*In at a time of 4 hours thus when applied to the formula in indent (iii), Iz>In/0.725.  

    However, referring to Appendix 3 for 5A,15A and 30A 3036 fuses, the value I2 seems to be as good as a similarly rated BS88-2 or 88-3 fuse . I2 for other In values of 20A, 45A and 100A 3036 fuses do seem to have a much extended I2 time. 

    So is the 0.725 correction factor applicable to some, but not all, 3036 fuses?

Children
  • It's simpler than 'calculating' ... Clause 7 of BS 3036 provides the answer:

    So, to convert the fusing factor of a modern device (1.45) to 2, uses a factor of 0.725 (or, 1.45 ÷ 0.725 = 2)

    I understand the derivation of the correction factor of 0.725 as it comes from the declared fusing factor of a 3036 fuse of 2*In at a time of 4 hours thus when applied to the formula in indent (iii), Iz>In/0.725.  

    The time for the fusing factor test according to BS 3036 is not 4 hours, but varies up to 2 hours according to Table 5 of the standard:

    Not that it makes a lot of difference when you look at the time-current curves ... 'calculated from lookup' values of 1.7 ish upwards towards the limit of 2 are seen if you were to use the graphs. Of course, we must consider that the actual fuse wire used will have variations. The time-current characteristics are captioned in BS 3036 as 'typical'.

  • I suspect that some confusion is coming from texts like this one.

    BS 3036 semi-enclosed fuses cannot be relied upon to operate within 4 hours at 1.45 times the nominal
    current of the fuse element.

    From https://electrical.theiet.org/media/1611/semi-enclosed-fuses.pdf

    But this is firmly in the 'may or may not' blow grey area. In effect depending rather on the holder design, and how much heat can soak out of the wire, "30A" fuse wire will carry 30A for ever, but may or may not also carry 40 odd amps almost for ever as well. The only sure fire thing is that within 2 hours at 60A it really should have let go, but it may well do that a lot faster.
    The problem with rewireable fuses is their inherent lack of consistency, and even for the same model of holder, being dependant on how the wire was fitted and perhaps how much it was abused at the ends.
    The trick is not to rely on rewireable fuse for anything that really needs close protection - and most things don't.

    Mike.