Advice on ATEX glanding.

Good evening and thanks for looking.

I've had a look at a brand new piece of equipment that needs to be maintained in the coming months. The threads on Exd glands into threaded housings in zone 2 IIC have been coated with copper ease, I understand a non conductive lubricant can be used on threads but I would expect the copper ease to be conductive. Am I right to be concerned. Thanks

Parents
  • Was the copper grease applied by the manufacturer / installer?

    What is your thinking behind the need for a non-conductive grease?

    You wouldn't be confusing this with the need for a non-setting grease to be used on Ex d enclosure flanges, where required?

    - Ross

  • As you have mentioned that the piece of equipment is certified for gas subdivision IIC, is there any risk of acetylene being present?

    - Ross

  • Hi Ross

    Thanks for your reply.

    Copper ease has been applied by the manufacturer.

    A lubricant is used to stop galling to the threads between two stainless steel fittings.

    I recall 60079 having information about grease being non conductive but I may be confused with non-setting. I'm on site and don't have access to all my standards and guidance at the moment.

Reply
  • Hi Ross

    Thanks for your reply.

    Copper ease has been applied by the manufacturer.

    A lubricant is used to stop galling to the threads between two stainless steel fittings.

    I recall 60079 having information about grease being non conductive but I may be confused with non-setting. I'm on site and don't have access to all my standards and guidance at the moment.