Thank you Mike,
The volatges are only sitting about 253 -256 volts maximum, the DNOs as said will do very little, citing it is within their tolerances.
As stated, the whole issue is around the fact we cant at resent turn the voltages up unless compliant with IET-01, for the goverance that, that gives us.
uWell, "compliant with IET-01, for the goverance that, that gives us." is only a thin top cover- legally think of it like the OSG non binding advice to charger manufacturers.
I hope/expect it to become more formalised over time, and before becoming a standard, to have these sort of wrinkles ironed out.
But right now,
"IET 01 is not a designated standard. The IET make no claim that IET 01 is a designated
standard or that IET 01 can be used as a ‘presumption of conformity"
as per
https://electrical.theiet.org/media/0wvdbopm/iet-01-frequently-asked-questions.pdf
Even if it was, it only applies to systems that rely on the correct operation of an O-PEN for human safety.
So I'd argue, if you can't use that method, then don't, but do meet the relevant British or international standards another way instead.
i.e. follow the maker's advice, and if nervous about that add any alternate means detect loss of neutral and use that to kick off the supply.
Mike.
uWell, "compliant with IET-01, for the goverance that, that gives us." is only a thin top cover- legally think of it like the OSG non binding advice to charger manufacturers.
Same as if published as a PAS ... or even a British Standard that's not a Designated standard.
Only Designated Standards are afforded presumption of conformity ... that doesn't mean other standards can't be used.
"IET 01 is not a designated standard. The IET make no claim that IET 01 is a designated
standard or that IET 01 can be used as a ‘presumption of conformity"
Quite ...
The issue is there is no other standard for the functionality at present, so it's up to the manufacturer to put everything relevant into a technical file - given that IET 01 is more than simply a standard to check the device is reliable, meets EMC requirements etc, which perhaps points to the depth of information necessary for a technical file for functionality not covered by a product standard?
I suppose IET 01 is not the only way - relevant parts of other standards could also be compiled to provide a similar set of information?
WOW- I looked at the preamble to IET-01 quoted in this discussion and found a indirect relationship to another current discussion Titled "Earthing and Bonding advice flooded Mobile Steel Training Unit " by Rob Phillips.
The other interesting item is that the IEEE Spectrum April 2025 on pages 33-37 and page 47 has an article by Wally Rippel and Alan Cocconi that identifies a cheaper and simpler-and just as safe "double ground" circuit that prevents shocks for EV Chargers.
Peter Brooks
Palm Bay FL
The other interesting item is that the IEEE Spectrum April 2025 on pages 33-37 and page 47 has an article by Wally Rippel and Alan Cocconi that identifies a cheaper and simpler-and just as safe "double ground" circuit that prevents shocks for EV Chargers.
Article here I believe https://spectrum.ieee.org/ev-charging-2671242103 ??
Two lots of earth electrodes ... and still need to separate from PME ... both potential issues here in the UK (space for electrodes, striking underground services etc., also PME widespread).
I looked at the preamble to IET-01 quoted in this discussion and found a indirect relationship to another current discussion Titled "Earthing and Bonding advice flooded Mobile Steel Training Unit " by Rob Phillips.
Discussion here; Earthing & Bonding Advice Flooded Mobile Steel Training Unit
Although, not sure why this relates to OPDDs? BS 7671 does not, at this time, recognize that approach for mobile & transportable units (Section 717) or indeed anything other than EV charging in Section 722.
However, there are devices on the market that monitor for symptoms of open PEN and open neutral conditions that would let operational staff know of an issue so they can act to make safe or repair when necessary?