Domestic 2 phase system and additional single phase supply.
Hi everyone, a domestic refurb has an existing 2phase supply. The DNO cut-out is arranged like a standard PME system. Is it reasonable to use the same earth terminal for both phases. I guess this is the same as what would be standard for a 3phase system, only in this instance 2phases. Additionally our client has applied for another single phase supply that is to enter site at another location, therefore 2 supplies onto one site. The DNO seem happy with this though I find it unusual as commercial projects do not seem to like two PME supplies onto one site?
  • This needs to be considered along with the requirements for the swimming pool.
    engx.theiet.org/.../special-locations-pool-rebar-bonding
  • Yes the same earth terminal can be, and SHOULD be used for both phases.
    As regards two PME supplies to the same premises, this is discouraged, though not totally prohibited. Precautions include, linking together the two PME terminals with a cable at least equal to the two incoming CNE conductors. This cable to be green/yellow with blue markings at the connections. This blue marking warns that the cable may be carrying diverted neutral currents.
  • Two phases from three-phase or two phases from split-phase or possibly even two supplies from a single-phase?
    What is the voltage across the phases?
  • not seem to like two PME supplies onto one site
    Depends what's meant by "site" - if it's to two separate buildings situated well apart but just happen to be on the same farm for instance, that's likely to be fine. If it's two supplies into the same big building with lots of shared metallic pipework or structural steel, that's much more likely to be a problem. It's the somewhere in between that gets tricky...
    Some DNOs do have ways around this sort of thing - e.g. having one common PME point outside the site, and running PE and N separately from there to each intake position. It's still PME, but avoids the worst of the diverted N currents problems.
  • Any scope to ignore both company electrodes and make it 'TT' ? Eliminates the other problem with the pool in one stroke.
  • Thanks for the reply Broadgage,
    I didn't realise you could progress two PME connections by linking the two as described.
    My usual method would be to set the second supply up as a TT system.
    Steve
  • Thank for the reply Sparkingchip,
    We've not checked the voltage across the two phases yet, when we do I'll let you know.
    Whilst the service head supply side of the ISU has 2 phases, the current building is wired on one phase.
    We will need the second phase for the additional load.
    We originally advised to make a new 3phase application, though have been advised there is no 3phase available on the local network for 200m, which would involve high costs for new connection, civils costs and navigating local streams / becks.
    Steve
  • Hi Mike,
    Yes my bolt and braces approach would be a TT system, especially when considering the pool hall problem.
    If providing a TT system allows not to bond the rebar, therefore avoiding the need to damage the slab, then this has to be the preferred option.
    As mentioned in the other thread, it will be interesting to see what the lightning protection / earthing specialist comes back with.
    Steve
  • We originally advised to make a new 3phase application, though have been advised there is no 3phase available on the local network for 200m, which would involve high costs for new connection, civils costs and navigating local streams / becks.
    Seems most likely you have a split-phase setup then (460/230V).
  • likely you have a split-phase setup then (460/230V).
    I agree, and if that is so you will need to either install 2 single phase consumer units for 230V, or convince yourself that one intended for 3 phase 230/400 is in fact no risk at all with 460v between phases .
    In practice it will always be fine but not all designs are actually rated for split phase  by their makers. The phase to phase PSSC is slightly higher than the equivalent phase to phase on 3 phase for the same single phase loop test readings.