TN system for generator

This is the resistance (281 ohms) of the earth electrode connecting star point and frame of a stand alone TPN gen set. It was one of 15 used at a recent outdoor festival. I do appreciate the desire to keep the resistance within the norms usually applied, say around 20 ohms, but I don’t think there is anything in BS7671 that puts numbers on a TN system. I am not looking to debate the merits of such earthing or how this value could be reduced. I guess my question is more concerned about the value of earth resistance that the “T” in TN-S remains legitimate as far as 7671 is concerned. Is it solely related to some value that will ensure RCD protection will operate?

Parents
  • This is the resistance (281 ohms) of the earth electrode connecting star point and frame of a stand alone TPN gen set. It was one of 15 used at a recent outdoor festival. I do appreciate the desire to keep the resistance within the norms usually applied, say around 20 ohms, but I don’t think there is anything in BS7671 that puts numbers on a TN system.

    Not that I'm suggesting we can apply a draft standard, but out of interest, the latest Draft for Public Comment for BS 7430 (see here, comments period closes on 10 September) steps away from 20 Ω in cases where generating sets are supplying an installation, and all circuits are protected by RCD, and recommends 200 Ω for TN system (Clause 6.1, Table 1). Where OCPDs are used, the recommendation of Clause 6.1 remains 20 Ω.

    200 Ω is of course provided as a recommendation as above this value it's generally accepted that the earth electrode might not be stable.

    20 Ω is a lot more interesting ... probably the true "source" is legislation and UK supply industry practice, particularly around PME ... interestingly, an earlier value used was 10 Ω.

  • Thank you GK, at least that gives me some idea of a number. However, it would be a blessing if someone could explain the engineering rationale of the 200 ohms for RCD protected arrangements as distinct from 20 ohms for those without.

  • the engineering rationale of the 200 ohms for RCD protected arrangements as distinct from 20 ohms for those without.

    Maybe I'm being unfair, but my suspicion of the underlying logic would be something along the lines of "20 Ohms can ****** difficult to achieve and isn't really justifiable - while 200 Ohms is a well recognised number (not from any direct electrical calculations, but from a stability across the seasons point of view) and reasonably achievable in the majority of soils ... so what excuse can we come up with to justify a number that's 10x higher than the standard (BS 7430) says...

      - Andy.

  • Well both 20 and 200 ohms seem to be a peculiarly British thing.

    There are a number of real considerations however. One is British soil. If you move to the middle east, or even Malta, the chances of getting anything as low as 20 ohms  with a sensible cluster of electrodes is almost nil. Whereas in the UK in Essex clay it is quite practical to hit 20 ohms with a couple of 4ft rods. Of course where I am in Hampshire, the ground is sand and gravel, and in the recent dry spell a similar 2 rods managed about 300 ohms but ho hum.

    So practically to blow all but the smallest fuse or trip a breaker in any sensible time, relying on a loop with 2 electrodes - one intentional at the genset, and the other accidental at the fault, is a pretty long shot, even for a 5A MCB on a lamp post - which is the sort of thing the 20 ohm figure seems to come from, or rather if 5A is diverted into a 20 ohm electrode, the step voltage is about 100V - and much more than that is getting more than a little dangerous..

    Before my time, I'm told, the way to verify the earth on a TT house was to put a 60W lamp between live and electrode and see how bright it lit. A dim light or no show indicated a bad earth.  So, what sort of value was that checking for ? well a 60W lamp draws 1/4A and is noticeably dim by 200V(?) so if we said 50V dropped at 1/4 amp, that would be about 200 ohms. Hmm. (there are some nasty approximations here, as the filament resistance falls when it is dimmer, but of course the current is not constant.)

    Enter the RCD, now we can have a 'safe' step voltage of say 50V near the electrode at our largest non disconnected fault current  (30mA/100mA or 300mA depending on RCD) so the resistance to terra-firma can be 1.6k ohms /500 ohms or 160 ohms . Well the 160 ohm case needs real electrodes, but the 30mA one will be happy with a screwdriver or a garden fork in the lawn, and now we credibly are protecting the person with wet feet picking up the severed lead to the hedge trimmer or whatever.

    But a high resistance electrode is not good, as if unlucky you can have a fault that is much better earthed than the genset - a live core being spiked by a metal fence comes to mind, and also the falling of a 3 phase connector into a ditch full of muddy water. The 230V is shared between the 2 'electrodes' with the bulk of terra firma at the mid point, and it is possible for the genset and all CPCs to be elevated to most of the supply voltage wrt the ground beneath your feet.

    its arbitrary but worth thinking of the likely fault cases.

    Mike.

  • So practically to blow all but the smallest fuse or trip a breaker in any sensible time, relying on a loop with 2 electrodes - one intentional at the genset, and the other accidental at the fault, is a pretty long shot, even for a 5A MCB on a lamp post - which is the sort of thing the 20 ohm figure seems to come from, or rather if 5A is diverted into a 20 ohm electrode, the step voltage is about 100V - and much more than that is getting more than a little dangerous..

    Agreed, although the discussion is about TN-S, in which the electrode (and the ground it is in) does not partake in the fault path itself for ADS.

    However, for additional protection, the ground and the source earth electrode might be used as a "return". In this case, provided an RCD with residual current rating not exceeding 30 mA is likely to operate, all is good.

    Enter the RCD, now we can have a 'safe' step voltage of say 50V near the electrode at our largest non disconnected fault current  (30mA/100mA or 300mA depending on RCD) so the resistance to terra-firma can be 1.6k ohms /500 ohms or 160 ohms . Well the 160 ohm case needs real electrodes, but the 30mA one will be happy with a screwdriver or a garden fork in the lawn, and now we credibly are protecting the person with wet feet picking up the severed lead to the hedge trimmer or whatever.

    Agreed

    But a high resistance electrode is not good, as if unlucky you can have a fault that is much better earthed than the genset - a live core being spiked by a metal fence comes to mind, and also the falling of a 3 phase connector into a ditch full of muddy water. The 230V is shared between the 2 'electrodes' with the bulk of terra firma at the mid point, and it is possible for the genset and all CPCs to be elevated to most of the supply voltage wrt the ground beneath your feet.

    Also agreed.

    In fact, guidance for some time has been pointing installers away from "earth rod does the job" to the use of earth mat or conductive disc type electrodes for a number of reasons (including reducing the risk of buried services strike, which, in the case of gas, can be very nasty). Having said that, for temporary installations in a field or similar, well, it's going to be some sort of rod isn't it?

  • Having said that, for temporary installations in a field or similar, well, it's going to be some sort of rod isn't it?

    I'd agree for general garden fetes and so on. 
    Or rely  the skids of the genset if the ground is wet, but the sort of scouty event I do, involve so many spikes in the ground, that a few more make no odds to the risk, The sort of things you use to secure a marquee or a climbing tower are probably better electrodes than the official electrodes.

    For some mil stuff we have plates that you drive on that go under the fronts wheel of the vehicle and get pressed into the earth,  these are more popular if there is a risk of buried munitions... some of the stuff I have been involved with  in the past has had some unusual looking risk assessments.

    Mike.

  • If I read the HSE guidance correctly, they advise that even for large 3p gens used for short term events, there is no significant concern in not connecting frame/neutral to earth. That being the case, then perhaps hammering in electrodes could pose a risk that should be avoided altogether?

  • If I read the HSE guidance correctly, they advise that even for large 3p gens used for short term events, there is no significant concern in not connecting frame/neutral to earth. That being the case, then perhaps hammering in electrodes could pose a risk that should be avoided altogether?

    There is a very nasty fault scenario that can occur if you do that ... if a line conductor becomes connected to the ground somehow (e.g. long nail or tent peg or similar going through a flexible cable that only penetrates the insulation of a line conductor), then the frame becomes live with respect to the ground.

    I have been led to understand that this has killed a security operative on trying to enter a site portacabin with conductive outer fabric connected to the "mains earth" inside the unit.

    The current version of BS 7430 therefore suggests armoured cables are used for distribution with unearthed generating sets - this will operate protection to prevent the nasty scenario. 

    However, if flexible cables are supplied from, say, portacabins or other mobile/transportable units with unearthed generating sets, the same nasty issue is back again.

  • I think the 20 and 200 ohms proposed in the DPC version of BS7430 is a reasonable tack for gen sets at a festival event, particularly to address the "nasty fault scenario" that you describe. 

    That was the kernel of my original post. I wanted to establish the maximum electrode resistance that could legitimately describe a generator arrangement as TN. 

    My thinking was taken from the TN requirements for a public supply as outlined in the wiring regs in the ROI (IS10101-2020 A1 2024). 

    The designer of the electrical installation for the festival event I identified in my original post merely specified that the gen-sets were to be arranged as a TN-S system with adjustable RCD set at 300mA time-delayed to 0.5s (apart from the stage supply where he had permitted the RCD to be bypassed). There was no specification for the electrode resistance establishing the "T". 

    Often the electrodes that accompany the gen sets are thumped in with a few clouts of a sledge hammer without any thought of their intended function. In fact, the electrician in charge of this particular festival was a veteran of such events across the UK and Ireland said that it was rare that the electrodes were subject to test as we had done.

    Following the exactness required for a TN system for a public supply might be onerous and would obviously require speculation about the value of Re, however, as a way of reference for compliance at such events in the future, I will run with the recommendation in the DPC version of BS7430, as well, of course, by ensuring cables are of adequate mechanical strength and appropriately installed. 

  • That was the kernel of my original post. I wanted to establish the maximum electrode resistance that could legitimately describe a generator arrangement as TN. 

    My thinking was taken from the TN requirements for a public supply as outlined in the wiring regs in the ROI (IS10101-2020 A1 2024). 

    Don't these requirements revolve around TN-C-S? Which in the UK is where, I believe, the 20 Ω figure came from that ended up as a recommendation for all TN systems.

    The question that was posed in developing the guidance previously published in the IET CoP for Electrical Energy Storage Systems, that are now proposed for BS 7430, was 'Why should this apply to TN-S? Provided the connection with earth is low enough to operate RCDs for additional protection, i.e. residual current rating of 30 mA or less, in a TN-S system do we mind?'

    There is still not full agreement in the industry that 200 Ω is the threshold of instability ... there are discussions about it being too much in some cases, too little in others. However, I don't think anyone has an alternative reasoned proposal at this stage to reduce or increase the 200 Ω value.

  • I’ve been doing some reading of the HTM 06-01 regarding this.

    With reference to HTM 06-01 (2017) section 13.11 - generator earthing: 

    It should be ensured that an adequate fault current can be developed to operate any protective device within the electrical network

    This supersedes the resistance target (old 13.13) of less than 20 ohms. 

Reply
  • I’ve been doing some reading of the HTM 06-01 regarding this.

    With reference to HTM 06-01 (2017) section 13.11 - generator earthing: 

    It should be ensured that an adequate fault current can be developed to operate any protective device within the electrical network

    This supersedes the resistance target (old 13.13) of less than 20 ohms. 

Children
  • This supersedes the resistance target (old 13.13) of less than 20 ohms. 

    I don't agree with the logic that this means you don't need to meet the BS 7430 recommendation (generally 20 Ω for TN systems) if the system is TN-S or TN-C-S ... the earth electrode is not part of the earth fault path for ADS, so meeting the 13.13 requirement of HTM 06-01:2017 has nothing to do with the earth electrode !

    And in the latest DPC for BS 7430, the recommendation is still 20 Ω unless all circuits are protected by RCD (which broadly aligns with the IET CoP for EESS).

  • Hi Graham. Are you involved in the latest DP. For BS 7430?The previous edition of the HTM explicitly specified a 20-ohm value for earth electrodes, but this has been replaced with the new statement I mentioned. I understand that an electrode connection is essential to allow fault currents to flow back to the supply in the event of cable insulation failure (same way, the public distribution is earthed to detect the collapse of overhead power lines. ) The updated HTM no longer references the 20-ohm value for generator earth rods. Why do you think this is ?  

  • Hi Graham. Are you involved in the latest DP. For BS 7430?

    I am the current Chair of GEL/600, which is responsible for BS 7430.

    Also, see Page 5 of HTM 06-01 (2017).

    The previous edition of the HTM explicitly specified a 20-ohm value for earth electrodes, but this has been replaced with the new statement I mentioned.

    I agree the statement about an earth electrode was removed in the 2017 version of HTM 06-01, and at that Clause number there is another requirement.

    I understand that an electrode connection is essential to allow fault currents to flow back to the supply in the event of cable insulation failure (same way, the public distribution is earthed to detect the collapse of overhead power lines. )

    I would agree this might be the case in a public distribution system for overheads or cables not in the ground., but I think buried cables are different and require an earthed metallic screen ('protective screen') ... see Regulation 13 of ESQCR.

    BS 7671 doesn't recognise an earth fault path in a TN system that doesn't flow through exposed-conductive-parts and protective conductors ... except for additional protection where the fault path is not defined, only the maximum residual current rating of the RCD. 

    The updated HTM no longer references the 20-ohm value for generator earth rods.

    Agreed.

    Why do you think this is ? 

    Why repeat something that's covered in a British Standard (BS 7430)?

    See HTM 06-01 (2017), Clause 13.1, and the shaded note at the beginning of Section 9, which specifically call out the standard.

    With reference to HTM 06-01 (2017) section 13.11 - generator earthing: 

    It should be ensured that an adequate fault current can be developed to operate any protective device within the electrical network

    I don't think this is a replacement statement for a requirement for an earth electrode resistance of 20 Ω.

    In fact, why do we think it is? Surely, a fault to the 'general mass of the Earth' (or at least, to something metallic connected to the Earth with a negligible effective earth electrode resistance) will only provide an  maximum prospective fault current of 11.5 A ... which won't operate an OCPD of rating much above 6 A !!!

    Surely the statement in  HTM 06-01 (2017) clause 13.11 is as much about co-ordinating protective devices (RCD or OCPD) with the source of supply ... such as UPS's and inverters, or using a rotary generator or battery-backed static converter as an alternative supply to the grid, and making sure the protective devices are good for all modes of operation (connected mode and island mode)?

    Remember also, the N-PE connection (now 'system referencing connection' used to be 'Neutral bond' or similar term) has a resistance of its own that is different to that of the PE-Earth connection (the electrode itself).

  • Going back to the statement “The connection between a generating set and Earth must have sufficiently low resistance to allow adequate current flow for protective devices to function effectively”. For instance, in the unlikely event that the generator’s tails come into contact with the general mass of Earth, a resistance of 20 ohms back to the generator’s star point would be too high. As you mentioned, this resistance would not allow enough current to trip a 6-amp MCB within 0.4 seconds. However, generators used in critical applications, such as hospitals, are typically not equipped with MCCBs or ACBs (Generator main breaker)  that incorporate RCD functionality. So how do you ensure disconnection in this scenario ? 

  • “The connection between a generating set and Earth must have sufficiently low resistance to allow adequate current flow for protective devices to function effectively”

    A similar consideration seems to be associated with the requirements for isolating the neutral conductor on TN systems. If, the source earth electrode is allowed to be up to 20 ohms I fail to understand how protection could be arranged to operate unless by RCD.

    The wording is exactly the same in the ROI regs, IS 10101. 

  • So how do you ensure disconnection in this scenario ? 
    You don't, and you don't need to - it's not  a single fault condition, so long as all class 1 kit has a CPC, and everything without a CPC has suitable sheathing/ cladding/ enclosure or whatever to qualify as double insulated or equivalent protection.

    Double fault to danger - e,g, a live to case fault plus a broken CPC, or cable sheath and basic insulation both damaged are not considered likely enough to require action.

    'Additional protection' by RCD or earth fault relay is just that, additional.

    Mind you that cable plus sheath damage is actually quite a common double fault, and is the thinking behind BS7909 requiring RCDs for temporary wiring at outdoor events etc.

    Mike

  • For instance, in the unlikely event that the generator’s tails come into contact with the general mass of Earth,

    What is the means of protection against electric shock?

    • If the tails are in armoured cable, or metallic conduit or trunking, it's ADS
    • If the tails are insulated and sheathed, then it's double or reinforced insulation.

    But, more importantly, what if the tails come into contact with something metallic connected to the general mass of earth.

    For instance, in the unlikely event that the generator’s tails come into contact with the general mass of Earth, a resistance of 20 ohms back to the generator’s star point would be too high. As you mentioned, this resistance would not allow enough current to trip a 6-amp MCB within 0.4 seconds.

    Correct, I made this point. We could go to 1 Ohm (the old value from earlier Editions of BS 7430, the old "combined earthing resistance" that permitted connection of HV and LV systems ... but even that would limit the OCPD nominal current rating to 160 A or so !

    In fact, why do we think it is? Surely, a fault to the 'general mass of the Earth' (or at least, to something metallic connected to the Earth with a negligible effective earth electrode resistance) will only provide an  maximum prospective fault current of 11.5 A ... which won't operate an OCPD of rating much above 6 A !!!

    But that kind of fault is only considered by BS 7671 in the case of additional protection (RCDs), and NOT other means of protection addressed in Chapter 41, because there is, in general, always at least 2 "faults" needed to create a shock hazard.

    The connection between a generating set and Earth must have sufficiently low resistance to allow adequate current flow for protective devices to function effectively

    But in this case, does 'Earth' include the protective earthing system ("PE")? Otherwise, as above (discussion regarding what current is needed for OCPD to operate) we'd be in a right pickle?

  • I fail to understand how protection could be arranged to operate unless by RCD.

    Exactly, which is why it can't mean that. It must mean the combined earthing system (including PE). There is really no other explanation.

    I think it's as simple as the PE is connected to Earth, and the generator is Earthed to PE ... then the statement makes sense?

    If, the source earth electrode is allowed to be up to 20 ohms I fail to understand how protection could be arranged to operate unless by RCD.

    I think this says it all, but to support my point:

    ... and perhaps HTM 06-01 Clause 13.11 is really aimed at Regulations 411.4.1, 411.4.2 and 114.1?

  • It may be worth pointing out that the whole voltage of the cpc 'earth' and exposed metal  relative to terra-firma ('Earth' with a capital E as Graham denotes it) is also a great headache for designers of substations, and when using generating plant with a transformer that steps up to HV for distribution of some distance and down again where the load  is.

    There are several things that make it impossible to know the fault or shock current accurately , plus the added complication that the impedance of a person in the fault loop is a very variable thing and the rise of earth potential affects how much the near fields of the various earth electrodes can be overlapped, or if they should be interconnected.


    Then the preferred approach to co-coordinating electrode impedance and disconnection times is that  more or less captured in BS-EN 5022
    That is to start  with some assumptions about the human body.

    To which multipliers are applied for hand to hand or hand to foot or foot to foot etc 
    The situation is complicated by the fact that as the voltage increases, the skin is damaged and becomes more conductive

    Leads to

    (so implying much above 690V to earth the ADS can never be fast enough - not really true - after all electric fences have many kV but very much shorter duration)

    But the voltages can be much higher if one can assume various types of footwear or a gravel or other self draining surface adding resistance in series with the person. 

    The lowest of these  - 'not really insulating at all wet leather ' footwear, aligns very approximately with the familiar 0.4 seconds for TN systems at 230V, though that is also the no footwear case  and an assumption that the voltage at fault point is about half that of the unloaded supply i.e. when the CPC and phase line resistances are equal.
    all these curves share a kink between 0.2 and 0.5 seconds as that relates to the period of the human heartbeat, and how long the muscles can be shocked for without it losing its rhythm.

    This is only a side branch to the discussion, but may explain where the numbers come from, and why various authoritative documents don't quite line up, as assumptions vary.
    Mike