EICR C2 on missing RCDs on existing installation

I had an EICR done on my property which I let and currently has tenants in it. The previous EICR in 2020 came back with no observations, so I was very surprised that this time I got C2 on missing RCDs on the distribution board (411.3.3; 415.1), final circuits for socket outlets up to 32 A (411.3.3), concealed cables in walls (522.6.202 and .203) and lighting circuits (411.3.4.), cables passing through zones 1/2 (701.411.3.3.) and for location which requires IP-rating (701.512.2.).

I of course absolutely want to ensure electrical safety and full compliance with the applicable laws and standards in my flat. However I am surprised, that the installation which at the time of completion in 2008 was certified safe and also passed the inspection in 2020, has now suddenly become unsafe due to missing RCD. To my understanding it is rare, that standard updates are applied to existing installations to this extent, and in a manner that requires immediate and extensive updates carried out within 28 days (deadline given on the report). Would anybody be able to confirm if this interpretation made by the engineer is correct, and indeed all landlords in the UK are now required to update electrical systems in their properties, if the RCDs are not present? 

Thank you

Parents
  • Is it a ground floor flat or first floor. That will make a difference to the coding if you follow industry guidance BPG4 as socket outlets could be a C3 if not likely to be used outdoors. Also following BPG4 all of the other points quoted should be C3 other than the bathroom which is a little more complex as you have to have supplementary bonding in place or it is a C2 for lack of RCD and supplementary bonding + effective main bonding etc.

    The above aside even if they are C3, the upgrade has correctly been recommended by the electrician. If you choose to ignore that advice and there is a problem down the line where an RCD would have helped then the responsibility lies with you and not him.

    Gary

Reply
  • Is it a ground floor flat or first floor. That will make a difference to the coding if you follow industry guidance BPG4 as socket outlets could be a C3 if not likely to be used outdoors. Also following BPG4 all of the other points quoted should be C3 other than the bathroom which is a little more complex as you have to have supplementary bonding in place or it is a C2 for lack of RCD and supplementary bonding + effective main bonding etc.

    The above aside even if they are C3, the upgrade has correctly been recommended by the electrician. If you choose to ignore that advice and there is a problem down the line where an RCD would have helped then the responsibility lies with you and not him.

    Gary