EICR C2 on missing RCDs on existing installation

I had an EICR done on my property which I let and currently has tenants in it. The previous EICR in 2020 came back with no observations, so I was very surprised that this time I got C2 on missing RCDs on the distribution board (411.3.3; 415.1), final circuits for socket outlets up to 32 A (411.3.3), concealed cables in walls (522.6.202 and .203) and lighting circuits (411.3.4.), cables passing through zones 1/2 (701.411.3.3.) and for location which requires IP-rating (701.512.2.).

I of course absolutely want to ensure electrical safety and full compliance with the applicable laws and standards in my flat. However I am surprised, that the installation which at the time of completion in 2008 was certified safe and also passed the inspection in 2020, has now suddenly become unsafe due to missing RCD. To my understanding it is rare, that standard updates are applied to existing installations to this extent, and in a manner that requires immediate and extensive updates carried out within 28 days (deadline given on the report). Would anybody be able to confirm if this interpretation made by the engineer is correct, and indeed all landlords in the UK are now required to update electrical systems in their properties, if the RCDs are not present? 

Thank you

Parents
  • I got C2 on missing RCDs on the distribution board (411.3.3; 415.1), final circuits for socket outlets up to 32 A (411.3.3), concealed cables in walls (522.6.202 and .203) and lighting circuits (411.3.4.), cables passing through zones 1/2 (701.411.3.3.) and for location which requires IP-rating (701.512.2.).

    I'm not sure how 701.512.2 comes into this. That reg is about using equipment with a suitable IP rating in zones 0, 1 and 2 - it had no direct relationship with need for RCDs. As others have said, the lack of additional protection by 30mA RCD for dry internal areas is typically a C3 rather than C2, but a C2 (and hence an overall 'unsatisfactory' outcome) would be reasonable for socket expected to supply equipment outdoors and for bathroom circuits if there was no (or inadequate) supplementary bonding in the bathroom (ditto for room containing a shower). So it might be a case of the detail being a bit muddled, but the overall conclusion (unsatisfactory) being accurate enough (all depending on the details of this particular case, which we can't see, of course).

    Understanding the details correctly would be helpful when it comes to decide on what remedial action is required or desirable - on one extreme it might be as simple as replacing a socket with an RCD version (in the perhaps unlikely event that only one socket was likely to be used for equipment outdoors), to a simple replacement of MCBs with RCBOs in the existing consumer unit, to (at the other extreme) a complete consumer unit replacement (e.g. if the existing unit is an older model that doesn't have RCBOs available for it) - with several other options in between. There will be quite a few factors to take into account, many of which won't appear on the EICR. A second opinion by someone who can see the installation, is always good for that sort of thing.

       - Andy.

Reply
  • I got C2 on missing RCDs on the distribution board (411.3.3; 415.1), final circuits for socket outlets up to 32 A (411.3.3), concealed cables in walls (522.6.202 and .203) and lighting circuits (411.3.4.), cables passing through zones 1/2 (701.411.3.3.) and for location which requires IP-rating (701.512.2.).

    I'm not sure how 701.512.2 comes into this. That reg is about using equipment with a suitable IP rating in zones 0, 1 and 2 - it had no direct relationship with need for RCDs. As others have said, the lack of additional protection by 30mA RCD for dry internal areas is typically a C3 rather than C2, but a C2 (and hence an overall 'unsatisfactory' outcome) would be reasonable for socket expected to supply equipment outdoors and for bathroom circuits if there was no (or inadequate) supplementary bonding in the bathroom (ditto for room containing a shower). So it might be a case of the detail being a bit muddled, but the overall conclusion (unsatisfactory) being accurate enough (all depending on the details of this particular case, which we can't see, of course).

    Understanding the details correctly would be helpful when it comes to decide on what remedial action is required or desirable - on one extreme it might be as simple as replacing a socket with an RCD version (in the perhaps unlikely event that only one socket was likely to be used for equipment outdoors), to a simple replacement of MCBs with RCBOs in the existing consumer unit, to (at the other extreme) a complete consumer unit replacement (e.g. if the existing unit is an older model that doesn't have RCBOs available for it) - with several other options in between. There will be quite a few factors to take into account, many of which won't appear on the EICR. A second opinion by someone who can see the installation, is always good for that sort of thing.

       - Andy.

Children
  • Sarah

    There has been a requirment for socket oulets to be RCD protected where thaey could be used to supply equipment outdoors for decades before your flat was completed. 

    Is you flat on an upper floor?

    It is irrelevant  when your flat was completed, the inspectopr should inspect and test your electrical installation and compared it to the current edition of the IET Wiring Regulations not a previous withdrawn standard.

    For me sockets that could be used to supply equipment outdoors is a C2, sockets for general use C3, circuits in a bathroom or other room containing a fixed bath or shower with no supplementaty protection and no RCD protection C2, cables in a wall without mecachanical protection C3, domestic lighting circuit no RCD protection C3.

    I would be interested to see the inspection and test report in 2020?

    I would strogly recomend you get a qualified and comptent electrican to upgrade your installtion to a satisfactory condition so you can comply with the law, sleep soundly at night and not have to face me across a court room! It will probaly cost you less than one months rent.

    JP

  • Hi John

    the flat is at 4th floor and an extension lead of several meters would be needed, if electricity was to be brought to the balcony. 

    I find some relevance in when the flat was completed, as something installed in 2008 is much safer than an installation from let's say 70s, which are still around. But I am of course not claiming that this makes any difference from point of view whether they comply with today's standards or not. And of course if the flat had been completed after RCDs became mandatory and was now found to not have them, and the installation had been claimed compliant at the time of installation, that would be an interesting conversation to have with the people involved. 

    I have serious doubts of the competence (or motives) of this guy who did the inspection, as I asked him on Thursday to break his lump sum quote (which far exceeded one month's rent, and this is a one bedroom flat in London we are talking about) to line items & cost and give me sufficient detail on each, and he is yet to come back to me. I think another look and a quote from somebody who takes a bit more pride in his work will be a good idea. 

    Thanks,

    Sarah

  • And of course if the flat had been completed after RCDs became mandatory and was now found to not have them, and the installation had been claimed compliant at the time of installation, that would be an interesting conversation to have with the people involved.

    The 17th Edn was published in 2008, but the electrical installation may have been designed whilst the 16th Edn was still current.

    I think that it would be very useful to see a photograph of your consumer unit please.

  • It's in a development of five or six blocks and several hundred flats and mine was the last block that was completed and handed over. Originally move-in date was going to be in 2007, but it got postponed several times due to snagging issues. So it is certain that the design was made well before 2008. 

  • Well then, there must be an awful lot of neighbours with the same problem (unless they are occupied by the owners).

  • the flat is at 4th floor and an extension lead of several meters would be needed, if electricity was to be brought to the balcony. 

    Humm, that could be an "interesting" point. I think when talking about mobile equipment outdoors, most think of the likes of lawnmowers, or hedge trimmer - where long extension leads, the prospect of a single event cutting straight through to a live conductor and good contact with terra-firma  can defeat the usual methods of protecting against electric shock quite easily. While the description of "outdoors" would on the face of it include the likes of a 4th floor balcony, I can certainly imagine some would assume that the requirements for sockets intended to supply equipment outdoors wouldn't apply to a 4th floor flat. That might explain some difference of professional opinions....

       - Andy.