EICR C2 on missing RCDs on existing installation

I had an EICR done on my property which I let and currently has tenants in it. The previous EICR in 2020 came back with no observations, so I was very surprised that this time I got C2 on missing RCDs on the distribution board (411.3.3; 415.1), final circuits for socket outlets up to 32 A (411.3.3), concealed cables in walls (522.6.202 and .203) and lighting circuits (411.3.4.), cables passing through zones 1/2 (701.411.3.3.) and for location which requires IP-rating (701.512.2.).

I of course absolutely want to ensure electrical safety and full compliance with the applicable laws and standards in my flat. However I am surprised, that the installation which at the time of completion in 2008 was certified safe and also passed the inspection in 2020, has now suddenly become unsafe due to missing RCD. To my understanding it is rare, that standard updates are applied to existing installations to this extent, and in a manner that requires immediate and extensive updates carried out within 28 days (deadline given on the report). Would anybody be able to confirm if this interpretation made by the engineer is correct, and indeed all landlords in the UK are now required to update electrical systems in their properties, if the RCDs are not present? 

Thank you

  • going to get the RCDs done, but not by this guy who did the inspection.

    That is more or less what I might do in your shoes (if I was not the sort who would install the RCDs myself, and of course if my feet fitted your shoes - they may not) 

    However for the purposes of this, you may want whoever does the RCDs to  do the extra tests needed to create an inspection report at the same time - so you have the option to be be fully decoupled from the original inspection.

    It would be quite an odd installation for 2008 that has no RCD at all though at that point in time they were more expensive relative to labour.

    Thinking back, the tendency in small bedsits and so on was to have one RCD as the main switch so it all tripped off together - which was a nuisance if you lost the lights at night, but the thinking was that a torch or an emergency light could mitigate that.

    The half-way house that was also popular at that time in larger house sized installations was the so called 'split load' arrangement, with a single RCD covering several breakers for sockets, shower and any other things the installers felt to be at higher risk, and then anther group of breakers with no RCD for things like lights and fire alarms where it was felt the risk of tripping outweighed the additional safety advantage.

    RCDs are cheaper now, and appliances are less trippy, as makers are more aware of the problems. 
    Most installations are now either converting to RCBOs - that is a combined breaker and RCD device (the " RCBO" ) per circuit, or two or more RCDs, covering smaller  circuit groups that all have RCD coverage and a trip of any one group does not lose too much at once to be a problem.

    It is the way of things that what level is cost-effective protection changes, and the regs have gently tightened in that "may" becomes "should" has become "must". Although RCDs for sockets supplying circuits for outdoor use have needed an RCD since about 1983 or so , to have RCDs for all sockets at least has been the preferred option for years, long before 2008..
    Any way, do let us know how it goes, and if you want to post a pic of the consumer unit (breaker board) for a slightly more informed opinion and less waffle, please feel free.

    Mike

  • My comment was moderated as well even though I did not list it as helpful 

  • Yes. This Open University article describes the rules of statutory interpretation well. The rules are the same elsewhere in UK.

    Thank you for providing the link.

    I notice there are other options than the literal interpretation discussed, which may well permit a court to cover the other points I made if they were deemed applicable, but I am very happy to hold my hand up here and say that I am none the wiser as to which of the "rules" discussed in Section 3 at the link might be applied when ... this is not my expertise, so I will leave that to the legal professionals.

    So, whilst this is Welsh law, it does demonstrate the legislature's capacity to amend statutes when circumstances change.

    I agree, there must be a reason why it has not been deemed necessary to update the ESQCR since 2008

    The earlier standard may not have considered or mentioned an ISOD, but unless it prohibited it in some way, couldn't current devices be said to effectively comply with both versions of the standard

    I think that Andy has squared the circle.

    Further on ESQCR, I'm not aware of any "relaxation" of provisions of BS 7671:2008 to the present version of BS 7671, so yes, this is probably a non-issue.

    However, with respect to plastic ISODs, these are clearly not permitted by Clause 12.9 (my highlight) of BS 1363:1984 incorporating Amendments 1 to 6 (1990), which is the version of the standard cited in the Plugs and Sockets (Safety) Regulations 1994:

    12.9 Plug pins shall be of brass. Materials other than brass shall not be used in the construction of plug pins except for sleeves of pins as specified in 12.16. Plugs fitted with solid pins shall comply with 12.9.1. Plugs fitted with non-solid pins shall comply with 12.9.2.

    ISODs were not introduced into BS 1363-1 until 2003, although a route to market was available earlier than this through tests carried out in applicable test laboratories ... 


  • Well then, there must be an awful lot of neighbours with the same problem (unless they are occupied by the owners).

  • I notice there are other options than the literal interpretation discussed, which may well permit a court to cover the other points I made if they were deemed applicable

    Usually if the words are unambiguous, they have to be followed, but technology can mess things up a bit.

    Schedules 4 and 5 of The Road Vehicle Lighting Regulations 1989 require that a motor vehicle with four or more wheels first used before 1st April 1986 have headlamps with a minimum power of 30 W. Schedule 1 exempts vehicles first used before 1st January 1931 because they do not require headlamps (and never did).

    That was fine until LED lamps became available as replacements for filament lamps.

  • I'm not aware of any "relaxation" of provisions of BS 7671:2008 to the present version of BS 7671

    I think there have been a few minor ones over the years (this is from memory so not necessarily between those two versions)..  sockets 2.5m away from a bath/shower rather than 3m, PME allowed for EVSE in a few situations were it wasn't before, outdoor circuits not necessarily needing a 0.4s disconnection time (e.g. for distribution circuits) (I think they did in the 15th), omission of supplementary bonding in bathrooms, omission of main bonding outside of buildings.

    Granted the relaxation often comes with some mitigating new measures (RCDs, O-PEN devices etc), but still it would have been difficult to demonstrate compliance with the earlier standard at the time even if the mitigating measures had been foreseen.

       - Andy.

  • the flat is at 4th floor and an extension lead of several meters would be needed, if electricity was to be brought to the balcony. 

    Humm, that could be an "interesting" point. I think when talking about mobile equipment outdoors, most think of the likes of lawnmowers, or hedge trimmer - where long extension leads, the prospect of a single event cutting straight through to a live conductor and good contact with terra-firma  can defeat the usual methods of protecting against electric shock quite easily. While the description of "outdoors" would on the face of it include the likes of a 4th floor balcony, I can certainly imagine some would assume that the requirements for sockets intended to supply equipment outdoors wouldn't apply to a 4th floor flat. That might explain some difference of professional opinions....

       - Andy.

  • I think there have been a few minor ones over the years (this is from memory so not necessarily between those two versions)..  sockets 2.5m away from a bath/shower rather than 3m, PME allowed for EVSE in a few situations were it wasn't before, outdoor circuits not necessarily needing a 0.4s disconnection time (e.g. for distribution circuits) (I think they did in the 15th), omission of supplementary bonding in bathrooms, omission of main bonding outside of buildings.

    So perhaps there are technical anomalies for some installations, which might require a different view in a court case?


  • The level of detail on the work he quoted was in lines of "bathroom lights not IP rated, replace with IP-rated ones." I would certainly like to know the IP rating he is proposing to install, and also claiming 'not IP-rated' (as if they were fully exposed) when talking about LED-spots integrated within the ceiling is not professional.

    Now that we know more about the flat, this sounds very dodgy.

    701.512.2 says, Installed electrical equipment shall have at least the following degrees of protection: (i) In zone 0: IPX7 (ii) In zones 1 and 2: IPX4.

    Had the flat been in the attics of a Victorian conversion, the observations would have been more credible, but not in purpose-built blocks. I assume that the ceilings are higher than 2.25 m and that the shower outlet is below the ceiling, in which case the luminaire is outside the zones.

    It would not surprise me if RCD protection has been installed.