Requirements for an electrical design & the EIC

Hi All

Just a quick question, is it a legal requirement the following section to be signed? The main contractor, sub-contracted a designer and the employed a installer, however hey signed all sections apart from the design section. I can't remember it being a legal requirement but the MC can sign it as a departure?

I/We being the person(s) responsible for the design of the electrical installation (as indicated by my/our signatures below), particulars of which are described above, having exercised reasonable skill and care when carrying out the design and additionally where this certificate applies to an add1t1on or alteration, the safety of the existing installation is not impaired, hereby CERTIFY that the design work for which I/we have been responsible is to the best of my/our knowledge and belief in accordance with BS 7671 :2018, amended to ….. except for the departures, if any, detailed .as follows:  

Thanks

Heera

  • Quote from your spec

    "

    5.3 Detailed Design

    Notwithstanding the dimensions given within the Particular Specification the Contractor shall confirm by measurement on site the requirements for all cabling and plant provided within the Contract. Cabling and plant shall be provided compatible with site measurements.

     

    The detailed design shall include, but not be limited to:

    • Cable sizing calculations to ensure correct sizing, type, length and method of installation in the light of the plant and installation provided.
    • Cable installation design calculations shall take into account ambient temperature in compliance with BS7671 (see Guidance Note).
    • Finalising all cable routes including sizing of cable containment (ducts, tray, trunking, conduits, etc) including mounting arrangements.
    • All cable sizing calculations and test sheets shall be produced using the Amtech Pro Design software. Final test results shall be recorded on the Fast Test Plus format. Electronic copies of the design and test results shall be handed over to the Project Manager on completion.
    • The Contractor shall submit calculations to the Project Manager showing that the installation complies with the IEE wiring regulations. On completion of the installation the Contractor shall provide Completion and Inspection Certificates in the form prescribed in the IEE Wiring Regulations"

    Who did the Amtech calcs?  Did the project manager receive them? Are they documented? I know this bit is contractual but surely whoever did it designed it and their signature is needed on the form.

  • The bit that most miss (as registration applicants) is that they fail to say what they DID, rather than what they were `Responsible` for. That is, how they avoided being as useful as a chocolate fireguard, as they say Grimacing (e.g. did they ever say 'No', or initiate extra actions/work/reviews.. - all the authority, but "Without initiative, leaders are simply workers in leadership positions" ). 

    Mind you, you can't beat a good cup of tea [HHGTTG]

    In the context of the EICR, those that test and record their figures for the installation have the easier time about signing for those results, but, as discussed, there's a bit of a bind about what compromises the design intent that is beyond the tick box compliance. Any system that is 'functional' (does extra stuff) starts to get confused between 'interface' specification compliance and the functional requirement, it's specification, and the verification of compliance

  • I remember something the tutor said to myself on my original C&G 2391 course and one of those satements that sticks with you for life!

    I think that we must have had a same tutor. :-)

    I think that you could just about have an EIC with no design if you replace a broken consumer unit like-for-like. Other than that, I struggle to think of anything more than minor work which does not involve an element of choice - in other words, design.

  • haha!!

    - " I only made the tea, and did nothing more complex when  I worked upon project XX "

    is not the same as 

    "I was the design authority for the self-test and fault reporting unit on project XX but I also made some tea on those days when the traffic was good & I was first one in the lab."

    We have probably both worked with both characters over the years,
    Mike

  • The parties involved only sign for the work under their control and responsibility, but  there needs to be a design, install and verification sign off.

    The EIC does contain a box for 'description and extent of the installation' ... which needn't be a "whole installation'. So, it is still the correct vehicle to use, even if you are only responsible for the design, installation, or verification, of only one circuit, or perhaps even a part of a circuit for which a MEIWC is not appropriate.

    Moreover, depending on the contract, a larger installation, building or premises might well, even when newly pressed into service, have many EICs.

    In my experience, on sites where there is more than one contractor providing electrical, M&E, security and comms works, planning for the "end game" is the best approach. Try to get agreement early-doors what is acceptable to the parties involved for partial and final handover, and the scope, format and responsibilities for relevant paperwork. Planning to succeed, and agreeing what success looks like, is always better than having to dispute whether or not one or more parties have actually succeeded. A QS I know, who is also a member of the Chartered Institute of Arbitrators, would call it "plan to get paid" - run your part of the the contract around the payment applications and key milestone events, and know what's needed for each.

  • I remember something the tutor said to myself on my original C&G 2391 course and one of those satements that sticks with you for life!

    1) How can an installer, install something to comply with BS7671 if there was no Designer? Doesnt matter if its a complex project or an installer just adding in one new circuit. Either the installer is given the design by the Designer and thus the EIC should be signed by that party or the installer is actually the designer, in that case the installer signs for both. Or as we see on some EIC's there are multiple spaces for designers to be listed and for their respective signatures.

    2) How can the verifier, verify an installation against BS7671 if it was neither designed or installed to that standard? So the verifier should be in possession of the design details and criteria and ensure during verification that what was proposed has actually been exceuted, or if site conditions, equipment etc changed since design was initially carried out they make sure that change still complies with BS7671. Again the verifier could of course also be the installer, but sometimes they may not be.

    3) There is in theory three** checks or levels of "quality" control to ensure an electrical installation is in compliance with BS7671.  The designer ensures as far as reasonably practicable based on all details from client, principal designer etc they have carried out their electrical deisgn work in full compliance with BS7671 so thats the first "Check". The installer then makes sure that what physically is installed on site, the layout, equipment, use etc etc is indeed as the deisgner was informed if not its redesigned by the designer or the installer to suit the change, the installer ensures the installation is in accordance with BS7671 as far as their work is concerned. So thats the second "Check". Finally the verifier is the third and final safety/quality/verification check against BS7671 to ensure that in their view the installation they are verifying is indeed designed and installed correctly to BS7671.

    That made sense to me in 1998 and still makes sense to me today.

    Yes, contract awards and who does what may be far more complex nowadays, but to me my logic above is still sound. The parties involved only sign for the work under their control and responsibility, but  there needs to be a design, install and verification sign off. world I work in can be lots of EIC's at the end of the project, but a EIC handed to myself with no signature against the design will be sent back to the electrical contractor if design was in their contract, or I will sign the design part myself if I was also providing a design element.

    Cheers GTB   

  • Light fittings installed by team one

    Fire alarm by team 1A but components selected by specialist contractors X 

    final circuit Cables selected and erected by .. 

    Plant room supplies and sub main selected  by team three installed by team 7

    special FX by ....

    Director of program ..

    tea made by... 

    you get the idea.

    To reduce it to 'Fred Bloggs is responsible for all of it ' may not be appropriate.

    I dislike the, "not my part of ship" mentality, but I can see that it may lead to efficiency and economy.

    In theory, there are checks and balances. Each signatory certifies, "the work for which I have been responsible is to the best of my knowledge and belief in accordance with BS 7671[date]".

    However, the installer, who is a bit dim, but has good hand skills says to himself (or herself), the designer has already signed to show that the design is in accordance with BS 7671; I installed everything in accordance with the design, therefore my work must also be in accordance with BS 7671.

    The inspector admires the installer's workmanship, does his tests, and writes down the results. Of course, it must be in accordance with BS 7671 because the designer and the installer both say so.

  • tea made by... 

    An important question. I often ask that as a PRA for CEng/IEng applicants. If they add "and I made the tea" to their competence examples, how does the example now read? [cf the whole assertion of the thread; someone else did that 'design' work..]

    Scope and context!

  • The Design box if signed, infers that you have designed the whole installation rather than just the one part which you have carried out work upon.

    I see no problem in somebody signing for a company (which is a legal person) even when different bits have been done by different personnel.

    If different parts of the installation have been put in by different companies, then multiple EICs are required: each company just signs for the work they completed.

    If you add a new circuit, you do not accept responsibility for what was already there save that the section between the origin and the new circuit needs to be capable of supplying the new circuit safely.

  • i agree the current forms cannot cover all cases well. But there is no prohibition on making a more complex record than the current signature sheet on  'prpo-forma' forms available from the IET and from  the providers some competent person schemes.

    As Graham points out the areas of responsibilitiy may well be decided at contract allocation, though I suspect the actual who installs what is later decided based on staff  availability on the day.

    There could be, and maybe should be, if we are honest  a consolidated record somewhere that reads more like the credits that roll up at the end of a long film, as on a large program with multiple teams, there is  a mix of local design decisions and then some over-arching authority deciding the  big stuff.

    Light fittings installed by team one

    Fire alarm by team 1A but components selected by specialist contractors X 

    final circuit Cables selected and erected by .. 

    Plant room supplies and sub main selected  by team three installed by team 7

    special FX by ....

    Director of program ..

    tea made by... 

    you get the idea.

    To reduce it to 'Fred Bloggs is responsible for all of it ' may not be appropriate.
    Mike.